Hi all,
I did some work on a house the other day that had a circuit for sockets which was cabled in 4mm to half way in the house the split of it to 2.5 up to the sockets. It had a 32a breaker. I'm aware that you can have a 32a 4mm radial but that the whole circuit must be in 4mm. Using 2.5 on...
Morning all,
As we know, you can run a spur on a ring final cct from the top of the 32a breaker. But can you run a single socket radial cct from a 32a breaker? essentially making it a spur but without the ring being present.
Thanks
Story short, if any of you SE chaps based around the Brighton area can supply a 40-50m 32a extension cable (so a 4-6mm flex with a 32a blue commando on each end) - NOW, TONIGHT - I know someone who'll gladly part with money for it in a catering emergency!!
PM me asap.
Hi
Circuit Info
32a B RCBO Feeding a Combi Boiler through a FCU in the airing cupboard of the bathroom.
Tested at 1/2 Passed tested at 1 > passed reading Oo 20.5 and 180o at 21.3
When testing at x5 the RCBO is tripping but my meter (kewtech KT63) is showing fail >50v
Im assuming that this...
ive been having a dispute with another electrician about using 30A JB's on rings
a ring is made up of 2 legs of 2.5mm T+E,
2.5mm T+E ref method C has current carrying capacity of 27A
now surely the JB has to be rated higher than the cable, but using a 30A jb although this is less than the 32A...
SplitJugular
Thread
30a
32a
cable
circuit
circuits
final
right
ring
ring final
under
Hi guys hope you can help!
This might be a stupid question but in your opinions do 32A 3ph IP67 sockets to feed some outdoor jet wash units at a car wash require RCD protection?
Doing a quote for a bloke who's shall we say a bit "careful" with his money. The integrated ones are about £300...
Got a machine at a job rated at 32A Max, I believe that it will be fine on a 32amp commando interlocked socket but i have been requested to fit a 63amp?
Does anyone else think it should be overrated to 63amp, considering its backed at the board by a 32Amp opd.
Quick question,
i have somehow inherited a problem.
i have a radial wired in 2.5 t&e
on the circuit it a mincer and a double socket.
at the moment the only thing that is plugged in the socket is a clock.
here is my problem; if a put a 20a breaker the mincer trips it out as soon as it starts...
Bit bored, boys in bed, beers in tummy and I thought I'd ask everyone why a 4mm radial is allowed to have a 32A MCB protecting it when its current carrying capacity is only above 32A when it is clipped direct or in free air?
I'm thinking diversity, but what if its your only circuit for...
Hope somebody can help me.
I am installing a couple of 32A 3 phase sockets in a factory unit and I am not quite sure if I need to have a local isolator for each one or if I can connect direct from the fuse board?
They are located within 2 metres of the board so not sure if really needed?
Any...
Hi guys was testing a board this morning and it had a 4mm radial circuit protected by a 32a mcb, the circuit came from the d/b and ran through metal trunking in the ceiling and then went into conduit and down inside a wall space ( not sore if insulated or not ), and then into dado trunking, regs...
Hi,
I`m looking for MK 32A 3pole MCB BS3871 or replacement. As far as I understand that I cannot get them anymore from the shops. Where can I buy them this days?
Regards
Struck me recently as to why we use 6mm T&E for a 32A cooker circuit, when generally 4mm (clipped direct) would be sufficient. Is this a historical thing with BS3036 fuses?
Hi can somebody give me some help with this one, a yard for porta cabin storage and external 32A sockets fixed around the perimeter although the sockets are rated at 32A they have 16A mcb's fitted in the enclosure. leads are then run out to test the cabins and do maintenance,although the cabins...
Just thinking about a kitchen circuit, How close would i be pushing a 32a rfc with washing machine, dishwasher, and two double sockets (likely to use kettle and toaster at the same time ) would 2x A3 circuits be more sensible?
Working on an installation today. Noticed a circuit which is not connected to my work (different circuit). 1.5mm T&E (Ref method A) for upstairs lights fed off (I presume a hidden JB as nothing is visible) a FRC and protected by a 32A MCB. It's not been fused down, at least no FCU visible. No...
Hi I was wondering what certificate is required for changing just one 32A mcb to 40A mcb. It for 8.5 kw shower replacement, 15 meter of wiring is existing 10mm2 clipped to wall and there is a 45A shower isolator in meter cupboard.
Hi Guys,
Can somebody shed any light on why socket outlets rated at 32Amps or greater do not require RCD protection under BS7671?
Presumably theres some maths behind it?
And presumably the only exception is in a TT earthing System?
Cheers chaps
I've been asked to inspect a shop and have found 4x 32 amp ring final circuits supplying socket outlets, all wired in firetuf 1.5mm twin and earth.
Actually all the circuits are wired in this stuff, there must have been a deal on at the wholesalers..
My concern is does this comply with 421.1.103...
Natt
Thread
32a
alarm
cable
capacity
circuit
circuits
consumer
current
fire
ring
wired
Hi as title says my engineer wants me to fit the above to protect ring circuits supplied from a crabtree c50 board, wants me to supply a rcd unit from a 32A mcb with 4mm singles and then supply the ring from the 32A 30ma rcd,
I think the reason for doing this is either you cant get crabtree c50...
Guest112
Thread
30ma
32a
aus
circuit
crabtree
current
mcb
rcd
supplying
unit
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.
OFFICIAL SPONSORS
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc