cpc

  1. J

    2.5mm flat cable with a sleeved CPC

    I recall seeing this a long time ago. Is it still available? Anyone know.
  2. W

    MICC CPC

    I was looking at a job all wired in pyro. The pryo goes into the metal backbox with no flying lead, no problem can sort that out. However on the downstairs socket it looks like there has been some modifications ar some point. Instead of the MICC being glanded its just taken into the back box...
  3. Dartlec

    Neutral to CPC low reading on lighting circuit EICR

    Typically the EICR I fitted in this afternoon because I'd hoped it would be fairly simple (new build home, 2007), turned out to be the only recent one that's thrown up a major FI. Downstairs lighting circuit, 1mm T&E, currently on a 6A MCB R1+R2 fine, insulation test L&N -> E an immediate...
  4. V

    CPC low R2 continuity reading ring final

    Hi, I've just been testing a ring final before installing an outdoor socket and I got an R1 and rn of 0.6, but instead of 1.01 for R2 I got a range of readings from 0.1 to 0.51 and it wouldn't settle down, so I couldn't continue the tests. I know parallel paths could cause a low reading, but...
  5. N

    No CPC on lighting circuit

    No CPC at switches or light points. All lights are class 2 so a C3 on eicr. But what do I write for r1r2, just a LIM? is that acceptable? bit confused on this.
  6. G

    missing lighting cpc

    Good Evening, I have failed an EIC test, C1 lighting circuit has induced voltage on light switch screws. The lighting circuit is on a split load CU non RCD side only MCB fitted. All switches and pendants have a connected R2 however the CPC conductor present does not connect to any Earth, its...
  7. DeanoRN

    NICEIC Certification Scheme Joining a CPC such a NIC or Napit

    Hi all, i was thinking about joining a scheme to be able to sign off my own work and be able to take on more work. I've been working for a company for a few years now and doin all kinds of work in under their banner but want to start doing my own side jobs like board changes etc but need to...
  8. V

    EICR - No Line or CPC Continuity on Ring

    Here's one I wasn't expecting on an EICR. Recently rewired and renovated 2-bed property (2015ish). Having an EICR as a new tenant to move in soon. No reported problems. I expected to be in and out in about 3-4 hours to be honest, and as expected I found nothing wrong until I began my ring final...
  9. C

    Round Up or Down When Selecting CPC

    When selecting a CPC, do I round up or down? For example, if I have 120mm2 actives do I select a 50 or 70mm2 earth? If a have 150mm2 actives, is 70mm2 enough?
  10. J

    Borrowed CPC for water bonding

    I've come across a house whereby the redundant immersion heater circuit (15A) has had it's CPC repurposed as a means of bonding the incoming water supply in the same cupboard. Irrespective of the CPC being undersized is this, in theory, allowed or must the earth bonding be clearly identifiable...
  11. L

    Use of cpc as functional earth in appliances

    some time back a customer rang up saying a tenent was getting shocks from a shower .Investigation revealed the problem lay with a broken cpc (caused by new insulation installers) resulting in a voltage of approx 27 v on the metallic parts of the shower .However the finger of blame was initially...
  12. K

    Continuity for Neutral and cpc in TNCS due to PEN conductor?

    Hi, I am struggling to understand one concept if anyone could shed some light. as TNCS has combined neutral and Cpc so if on the consumer side hypothetically if you check continuity on N+Cpc without disconnecting any conductor, do we get continuity of Neutral and CPC as on the supply side, its...
  13. Rockingit

    Tables for SWA armour cpc?

    In a former life on another forum as well as this one.... there were a whole heap of downloads that people had done as ready-reckoners for things like Cu eq for various armour sizes, R1R2 values on lengths.. useful stuff. I think I might even have generated some myself. Anyone have any...
  14. M

    UK Borrowing a CPC?

    I have been asked to wire up a new extension for a customer and during testing prior to starting I have found that both upstairs and downstairs lighting circuits have no cpc's. However, upon further investigation it appears that the downstairs lighting circuit has managed to "borrow" a cpc from...
  15. Z

    Eicr no CPC on lighting circuit

    Hello, I have been asked to do a eicr on a property that I have found to have no CPC in the lighting circuit. Just wanted to know if this constitutes a c2, or vat best c3. Thank you in advance
  16. J

    UK Sub Main Armouring Earthing Question Combined CPC and Main Bond

    Hi I have reviewed a few posts around this subject, but my question is not covered. I know that the Submain Earth has to be sized on the DNO incomer, not on the submain to the external building itself. My question is if I need two main bonds in the submain building, for example one for ground...
  17. E

    UK CPC missing on ring final

    Morning All, Currently carrying out an EICR and going through ring final steps with the following readings: r1: 0.31ohm rn: 0.32ohm r2: 0.03ohm Started taking sockets faces off to find that there is no cpc, only fly lead to metal patress box and steel conduit trunking. (See photo) When i...
  18. B

    1.5mm CPC on 6mm Cable

    Come across an old Installation with 1.5mm CPC on a 6mm Live conductors whilst doing an EICR. Not seen many of these, in everyones opinion perfectly acceptable if all R1 and R2, IR, Measured ZS test check out ok?
  19. ETradesmen

    CPC calculation

    Just got back from looking at a potential job. What a bodge up! I was called around to be asked to install an isolator for a sub main feeding a consumer unit which a car charger company will come off feeding their charger. New mains upgrade recently done and the previous electrician has bodged...
  20. C

    Twin and Earth CPC

    IEC 60364-5-54 states that phase conductors 16mm2 and smaller require a CPC of the same size, over 16 to 35mm2 a 16mm2 CPC and over 35mm2 a half size CPC is required. My questions is why am I seeing catalogs with harmonized twin and earth with reduced size CPCs over 2.5mm2? And why doesn't the...