I have been asked to give a quote to install some downlights in a kitchen, but there is no cpc in the light circuit. I appreciate the response by some is the world would end if I did that, but the circuit is RCD protected and the last IR readings on the ciruit were good when the board was...
Done a periodic on this a few weeks ago and back now doing remedial. This notice and the previous Report state there are no cpcs through the lighting. None of the roses have a cpc connected but there is at the conduit boxes they are mounted on in fact I have checked every light and there is a...
Hello,
Just getting ready for my first scheme assessment and am completing a board change to be assessed on.
Ground floor ring end to end readings. Its a 2.5mm ring T+E
r1 0.71
rn 0.72
r2 8564
I have had all of the sockets off to check for a loose connection.
The property has over the...
Hey Everyone.
Whats your thoughts on using a 3core & earth to run x 2 final circuits? I have x1 three core & earth feeding contactors for emergency lighting. L1- fed from a 6A mcb is feeding a switched pole on a NO contactor, L2- fed from a different 6A mcb also feeding a pole on a NO...
Ok, so there have been a number of threads on old lighting circuits with no CPC. Also noted that it’s a no no to borrow a route to earth from another circuit.
In this scenario I have two lights atop of brick gate pillars. I have good continuity and sound IR between the two pillars along with a...
First time posting so hope this is correct place? Been checking out a Customers Premises and all is good apart from 1 lighting circuit that feeds a bedroom and office. A CPC has been run but has been damaged/broken/cut somewhere en route to first light switch. (proved by using wander lead)...
Hi All,
Visited a job today and was asked to supply and DB in a outbuilding via a Socket in the garden....:eek: i said i was not happy to do so and it wasn't possible.
DB was suppose to feed 4 sockets 3 lights and a little plug in heater, Client claimed she was told by 3 previous electricians...
Morning..
I have a garage fed by 4mm, 2 core SWA. It is a 25m run from the CU. Can I use the armour as the CPC? The Main house is TT.
I have always used 3 core so have not come across this before. i am about to check my notes as I know I have information on this and will find the formula to...
Hi Guys, an old existing 25mm - TP & N SWA Supply cable is glanded (No Banjo) to a 3" Metal Trunking end cap, & the remainder of the circuit cables are contained in the same trunking forming the CPC back to the Distribution Board. With a method 2 continuity & an insulation test, can you be...
I'm in a vineyard. There is a 300m buried SWA from the ccu direct to a 2 gang socket.
I'm getting 247V across N and L at the ccu.... But at the socket I'm getting 100V across E and N and 147 across L and N.
Continuity as a radial tested ok
IR All over 500 M
Please list possible issues here...
I’ve been asked to add a couple of extra points to the single ring main in a flat. Building fabric is concrete, all of the electrical installation is steel conduit buried in the concrete.
I opened the consumer unit and could only see one CPC for a radial socket, as well as the main Earth. No...
Replaced a db on a tt system, but moved it about 1m.
All circuits were required on rcbo.
So I've extended cables.
Now one lighting circuit has no earth.
Obliviousy I know existing it's ok to have no earth if class 2 fittings, relevant sticker notices in place. BUT because I've worked on...
I installed a kitchen ring recently. Went back to test after the builders had finished and found that the CPC is broken somewhere inaccessible, everything else tests normal. I’ve got continuity on live conductors, and even with the broken CPC, each socket is connected to the CPC and tests with...
Went to fit new light fittings in a loft conversion today.
The existing ceramic half moon uplights were installed using 2 core flex buried in the plaster going I know not where!
I've come across 2 core systems in old peabody trust estates that where complient as long as double insulated fittings...
Good evening
I am currently a training to become an electrician. I do hold both initial verification and periodic testing qualifications however this is an issue I have never personally had to deal with and was never mentioned on any of my courses as often seems to be the case.
Basically I am...
Hoping someone can help me clarify something.
For plastic surface mounted back boxes, why do some have a small metal terminal for connecting the CPC, whereas others don't? Is it just a differemce in quality, or would you generally use the ones with the terminal for sockets, and the ones without...
Hi - been to fix a lamp today with a loose connection in the lovely terminal blocks. Then I noticed there's a brass lamp holder with no earth terminal and the earth is cut back in the wall. There's 4 of these fittings (8 lamps) in the room and they're probably all the same. Any suggestions for a...
probably a daft question to most of you, but in an 1.5mm fp200 is the cpc the same size or is it 1mm because my supervisor has told me it is the same as t&e but I’m pretty sure it is the same size :/ I’m trying to find it in the on-site guide..
Thanks Adam.