cpc | Page 6

cpc

  1. Andy-1960

    Seperate / Integral earth CPC on 400A supply

    This one might get the old grey matter going! 400A supply 260m run on ladder fed from BS88 fuses to sub main distribution board. Did a cable calc using our Trimble software (was Amtech) and looked at the option of using an integral earth or a separate earth so I could use a conventional 4c...
  2. J

    EICR code Split cpc on ring final circuit

    lost continuity on cpc of ring circuit, live and neutral fine all test fine. C2,C3,FI ?
  3. C

    E27 pendant no cpc down to metal fittings

    hello guys Client has bought fitting from online, metal cable cap at top with single twin flex dropping down to an e27 pendant with metal casing and no earth. I'm saying client can't use them what's your thoughts?
  4. S

    CPC screwdriver special offer

    For anyone interested CPC have a Wera 7 piece VDE Insulated screwdriver set on offer @ £12.98+ vat
  5. D

    CPC Size & Max Permitted Zs

    Looking through our periodic certificate that was completed by a 3rd party, I've got a few queries that hopefully someone on here can clarify. We've got a Schneider Prisma switchboard (S3/MSP 3.1) fed from 11kV/400V Transformer. - What is meant by MW for cpc size of 2/TP and 13/TP? - Is there...
  6. M

    EICR for a rented property with cpc on the lights.

    I have a EICR coming up where I am sure there is no CPC in the lighting circuit, the property is rented and I am sure all the outlets are class 2. Where do i stand? Should the circuits be rewired? C2 or C3? Thanks
  7. P

    Testing

    Does it matter which method (method 1 or method 2) you use when testing for continuity of the circuit protective conductors? Or is each method dependent upon which the type of circuit you are testing on ring or radial? I have been told that test method 1 is used for lighting and radial...
  8. P

    Continuity Tests

    Is the continuity test for circuit protective conductors, the same test for ring and radial circuits or is there a different test for each type of circuit? Also what is the difference between testing for cpc continuity and testing for continuity for ring final circuit conductors?
  9. P

    Continuity Tests

    Is the continuity test for circuit protective conductors, the same test for ring and radial circuits or is there a different test for each type of circuit? Also what is the difference between testing for cpc continuity and testing for continuity for ring final circuit conductors?
  10. G

    Help with CPC size

    Hi I am training to become an electrician. I have a problem to solve to work out the size of the CPC. My calculations say I would use 6mm and 1mm CPC. This can't be right, can it? Please refer to attached document for details.
  11. S

    Do I need to be a member of a CPC to sign of commercial works?

    Hi, I am a little confused and hoping for some help. I am a qualified JIB gold card spark and work with a friend (also qualified spark) as sole traders, we have subcontracted to company's for the last say 5 years doing commercial electrical and fire alarm installations. Now we are looking...
  12. codger

    Missing cpc in domestic lighting circuit

    Morning. A friend and I have been carrying out some EICRs on properties in our area. Recently, my mate has come across two houses in which the lighting circuits do not have any earthing at all. They have been run in twin and earth but the earths have all been snipped off at lighting points...
  13. J

    Shock overcurrent ignored in recommendations?

    It is my reading that doing impedance tests we like a nice low resistance in theory overall and especially for earth , both Ze and R1 or both R1 and/or R2. This makes a high potential fault current Uo/Ze, way above the allowed fuse sizes for a light circuit or many power too. So do wires really...
  14. akwoody2

    Sharing Cpc - Two Lighting Circuits

    Hi Chaps, Carried out a condition report today and found two lighting circuits using the same CPC, 4mm single. Seems the lighting never had a CPC and someone has added the 4mm at a later date. From what i understand the 4mm is ok but is it ok for two circuits to share the same CPC? Thanks in...
  15. Sintra

    Swa Cpc

    Sintra submitted a new resource: SWA CPC - SWA CPC Read more about this resource...
  16. bigspark17

    Submain 16mm t&e cpc chopped

    EICR.. 80 switch fuse in meter cupbord, 16mm t&e to cu with 6mm cpc chopped both ends and 16mm earth ran along side submain. zdb/pefc/pscc fine. bonding from db fine. i would never do this but struggling to find a reg number aggainst it :/ opinions appreachiated
  17. rustynails

    CPC outisde junction box

    Why was it so popular to joint the CPC's outside junction box back in the day, answers on the back of a postcard please? I guess they never made junction boxes with enough terminals.
  18. charlie76

    No CPC in lighting circuit

    Evening all. I have been asked to quote a landlord for a replacement bathroom light as the old ones bayonet fitting was broken, new pull cord as it was one from 1702 which had finally given up and replace the hallway light fitting as it was hanging off the ceiling. On inspection there are no...
  19. P

    SWA seperate CPC

    Hi guys, how would you code a SWA cable which feeds a DB within a commercial unit with no seperate CPC so only realying on the SWA strands as means of CPC
  20. G

    12v deck lights with cpc

    Hi all. Been asked to fit some decking lights, customer has bought 20 of the from ebay. 0.75 flex, three core. Initially i thought these were 230v, but upon connecting 12v across live and neutral they light. Are these just 12v but wired in flex with a LNE? Cheers.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top