Hi guys starting a new job testing commercial properties, i have passed my 2391 a few years ago and im just looking to refresh myself<
1: when doing an IR test on circuits protected by rcbo's to i have to disconnect both neutral and earth flying leads?
2: what are the flying leads on rcbo's...
nicsin02
Thread
connected
disconnect
earth
electricians' talk
help
neutral
testing
Hi Guys
Domestic - Old Hager Box 14 MCBs RCD Main Switch. Totally stuffed with wiring - not keen to disturb
Tested the Full L+N busbars to E. IR = 1.8 Meg b****r! So close to 2 Meg!
Tried L busbar to E -all trips off. 1.8 Meg!!!!!!!!! - had to disconnect RCD!
Tried each cct in turn L to E...
Piratepete
Thread
circuit
disconnect
electricians' talk
going
insulation
neutrals
problem
testing
Hi All,
Firstly I'll apologise for not trying to collate this with another thread, But thanks to my organisation skills I find myself short on time.
I'm currently at College and coming up to a assignment to do with testing etc. I understand pretty much all area's of testing, However theres a...
Domestic CU change, TN-C-S. Lighting circuit has an Extractor Fan with Electronic timer installed. When performing IR test on the lighting, should i just test the whole lighting cct between L & N (connected together) and the CPC - I do not want to remove the cover of the extractor to disconnect...
Why do circuits over 32A have a 5s disconnect time yet those 32A or less have a .4s disconnect time? I have read the relevant regs but do not understand why and cannot find the answer in my books
Morning all!
Just completed my two jobs for my NIC assessment. Confident in my work and all of my test results etc. Anyway assessor had a cancellation so has booked me in for this friday so just wanted to double check a few things that are playin on me a bit. Nothing major but just wanted to...
rob121
Thread
always
correct
disconnect
doing
earth
electricians' talk
help
testing
hi there
have a possible job customer wants 4 light fittings changed and replaced. circuit will be Tested and Minor Cert issued. Customer supplying light fittings.
i usually charge £ 30.00 so would £120 sound fair ?
Whilst looking at the supply intake at a house rented by my mate I noticed the Main earth which was clamped to the sheaf of the supply cable was disconnected, the service head is a TNCS, the main earth from each small 3036 CU goes to this head as well as the two main bonding conductors...
LlandrilloSpark
Thread
anybody
aus
bonding
disconnect
dno
earth
electricians' talk
reason
supply
Hi people,
Can any tell me what would make an RCD take a long time to disconnect, i understand they monitor the line and netural wires but what would make them take a long time to disconnect or not even trip when testing.
Many Thanks.
I install ovens into large supermakets, within the bakery area, and sometimes these units are hard wired, most are three phase, some are single, upto 100amp supply, i have been told the installation and testing cert is needed, but we would not change the supply, only exchange the machine for the...
borgmaster
Thread
aus
disconnect
electricians' talk
phase
qualifications
supply
three
three phase
Hi all, I've just been asked to disconnect a 3 phase compressor. Not having done this before is it just a case of power off, disconnect then power back on or is there something special I'm missing out or need to consider?
Regards.
lish70
Thread
3 phase
aus
charge
compressor
disconnect
electricians' talk
phase
registered
I have a customer with a 4 double socket ring main on a 32Amp MCB in thier Snug, R2 and RN are all Good but R1 is open Circuit. The CU has a 100mA RCD on A TNCS (need to change it to a 30mA) the house was refirbished about two years ago and dont think the builder got in a proper Electrician...
mos
Thread
advice
appreciated
aus
circuit
circuits
disconnect
electricians' talk
radial
socket
When testing Insulation Resistance or Continutiy on a 3phase Motor, do you need to disconnect the cables from the motor?
Or do you just test I.R to the starter, then I.R from starter to motor? (as the starter will be open when dead)
Would a motor come under "equipment vulnerable to testing"...
whazza22
Thread
3phase
dead
disconnect
electricians' talk
fused
heating
motor
s-plan
starter
testing
Howdi
I have a 32a ring that when I test the RCBO it won't achieve 40ms when tested at 5x in 0 degrees but when switched to 180 degrees it trips well within 40ms The Zs measured is 0.49 ohms the circuit trips at 1x okay so Im a little confused and am looking for help to point me in the right...
bearlyable
Thread
confused
degrees
disconnect
electricians' talk
phase
rcbo
rcbos
when
Hi
When measuring Zs on circuits do you guys leave the main bonding connected or disconnect it? Most of my testing books including GN3 say leave it connected, but another book by Anthony Hinsley says to disconnect it as it will introduce parallel paths (which I get) and that if left connected...
Hi there,
I have a ----y problem as follows:
I have a ABB disconnect switch Fused at 60A, supplying 3 phase 575V(North America) to a Power Cabinet.
The Power Cabinet has several motors and a 6000VA transformer, that steps down the voltage to 230VAC/120VAC single phase.
The Cabinet...
collin1443
Thread
aus
blowing
cabinet
disconnect
electricians' talk
fuse
fuses
power
problem
transformer
Chaps
I replaced a single socket for a double socket for a customer today, and whilst doing the IR tests noticed that the Line/Neutral reading was low.
The readings were:
L/N 0.95 Mohms
L/E 97.6 Mohms
N/E 87.4 Mohms
I checked and made sure that nothing was plugged in on the ring and noticed...
When testing IR on a circuit spplying some outside floods with built in pir's, Is there any other way other than disconnecting the p.i.r in the fitting's?
HI
Doing a test with a voltage detector/continuity tester on live PME/TN-C-S system installation at a socket outlet either with load and without the load shows voltage between live and neutral and live and earth but live-earth seems to be short circuited and the continuity tester indicates...
mikex79
Thread
circuit
continuity
correct
cpc
disconnect
electricians' talk
neutral
pme
short
switch
system