insulation resistance test on a EICR/pir
have read in 'unite the union guide to inspect and test'
test carried out with L/N joined to Earth and no need to disconnect loads/vunerable devices
pic1 to test whole insulation, shows link between L/N (incoming) at main switch with supply isolated...
Hi guys,
I would just like to ask if any one could look at my test procedure off the top of my head and give any advice or pointers or whether its too long winded or short. got an exam in 2 weeks so trying to drill it in to this thick skull :)
Many thanks
Safe Isolation has been carried out...
Hi all, Tested a lighting circuit recently and got live to earth dead short and neutral to earth dead short on insulation resistance all loads were still connected there was a fluorescent fitting on the circuit and signs of green goo in switches and ceiling roses and the MCB was not tripping. Do...
Lilyrose08
Thread
circuit
dead
earth
fault
insulationinsulationresistance
lighting
lighting circuit
live
resistance
short
until
Hello All,
I am to install some extra sockets for a customer on a relatively new build.
The insulation resistance test.
I tested at 250VDC between line conductors connected and earth and obtained a reading of 1.10 ohms (not megaohms)
Does this reading seem likely that a piece of equipment...
applesandppears
Thread
circuit
insulationinsulationresistanceinsulationresistance testing
resistance
ring
ring circuit
testing
Hi all,
Just a quickie. I carried out an insulation resistance test on a lighting circuit which only has two rooms consisting of 4 lights.
Live to earth and neutral to earth was fine but when I tested live to neutral I got a short circuit.
All the bulbs were removed so just wondering if...
Newbie90
Thread
insulationinsulationresistance
live
neutral
resistance
short
Hi All first post
I read that during the insulation resistance test of a 3 phase removal of the neutral incomer is necessary !
can some one please state the procedure for 3 phase IR tests
Thanks
Been to a Job this morning problems with RCD tripping, Global IR came back 0.016, Split circuits down and lighting tested (Including outside tested 0.018) however tested again 0.567 and then 1.03 each time the figure increases until it sits about 1.14. Testing done L&N - cpc and then N-Cpc...
When doing a CU change and lights have no cpc. Every room has class 2 dimmers and lights. ceilings are like 20 foot tall. How would you guys go about Insulation testing? L&n to cpc ain't an option and removing all lights and bypassing dimmers is consequently going to take some time... What would...
bigbaddave
Thread
cpc
dimmers
insulationinsulationresistanceinsulationresistance testing
lights
no cpc
position
resistance
testing
tests
Hi i`m new poster, qualified electrician but not working as one just using it for my home.
I have installed an extractor fan with low voltage light in en-suite and now have to do a minor works tests.
I have done the resistance test an my readings are
l/n 0.8
l/e 1.7
n/e 1.3
earth fault loop...
Job is to extend a kitchen ring circuit, and have a question about Insulation Resistance values.
Tests on existing ring (2.5/1.5 t&e) carried out and results as follows -
Ring continuity (end to end)
R1-R1 = .38W
RN-RN = .42W
R2-R2 = .64W
Continuity W
R1-R2 = .34W
Insulation Resistance MW...
Hi
Was wondering if you could clear up a few things I on't quite understand, I've been told it is possible to do an insulation resistance test on a live DC cable (Solar pv) by testing to ground. Is this right, and what voltage rating should I set the megger to?
Also on a domestic solar pv...
mikemack00
Thread
cable
electricians' talk
insulationinsulationresistance
live
resistance
Iam currently on a new build project and I've been carrying out some IR test prior to everything being boarded up. The construction is all timber frames with celotex ply and plaster board, I have connected up the kitchen ring with connector blocks to carry out IR tests and I have been getting...
Lilyrose08
Thread
circuit
electricians' talk
insulationinsulationresistanceinsulationresistance test
new
readings
resistance
test
Can anyone help me?
I've got an annual inspection this week
What's the procedure for carrying out an array insulation resistance with a Megger 1552?
Many thanks
Hi guys, I obviously know how to conduct a IR test but I'm just looking for a few tips, I was doing a lighting d\b today and obviously I never did a L-N test as it was a massive building and not feasible to disconnect all lamps. It was a triple pole +N mainswitch so I isolated the board, it is...
Title says it all really. I've just qualified and unfortunately my college bombed through IR testing but before I even touch anything I want to make sure I understand it thoroughly. Can anyone please compare what I've copied and pasted below to the diagrams and made sure I've understood it...
Sharkster
Thread
below
between
connected
electricians' talk
fault
insulationinsulationresistanceinsulationresistance testing
neutral
please
resistance
someone
testing
through
I have recently qualified and am coming towards testing a re-wire. I have fitted 30 low voltage downlighters with transformers. Apart from removing the bulbs do I need to do anything else before pumping 500volts through the circuits. ie will 500volts damage the transformers or are they removed...
iwire4
Thread
before
circuit
electricians' talk
insulationinsulationresistance
lighting
low voltage
resistance
through
transformers
voltage
volts
Hi all,
Could someone please help with a query I have?
At a factory I work in, we get a lot of damaged motors (due to it being a very wet environment), they are only quite small normally, varying around the 0.25-0.37kW size.
Normally when I test them, I remove everything so I am left with the...
ryanm
Thread
3 phase
electricians' talk
insulationinsulationresistanceinsulationresistance testing
motor
phase
resistance
testing
When I was at college our tutor told us a way of doing ins res testing to ensure that downstream devices that are still plugged in are protected from the 500v voltage applied.
For the life of me I have forgot what he said.
Can a nice chap fill me in?
Thanks guys.
in a cafe at present working and is a load of stainless steel in one corner for washing up etc..
i want to do a test to see if needs bonding
im nearly certain i I r test from earth isco to stainless steel in question and test @ 500vdc and if under 22k ohms it should be bonded,
is this info...