Can anyone tell me the latest regulation for RCD protection on socket outlets, I believe it's required for sockets up to 32A but I'm told it applies to all socket outlets, we have to install a 63A 5 pin socket located outside. Thanks in advance
Hi all,
After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone.
Customer wants to upgrade from rewirable CU to RCBO so fairly old wiring but no signs of cable breakdown or anything totally messy on inspection. This circuit basically holds...
When doing an EIC for an additional circuit (which only covers that circuit), does the 'main switch/switch-fuse/circuit-breaker/RCD' section refer to:
a) the MCB you're adding for the new circuit
b) the existing main switch (whatever it is) for that board
c) [if the DB the circuit is added to is...
With regards to Regulation 531.3. 3 of BS 7671:2018+A2:2022
Older AC type RCD's are prone to being blinded by dc leakage from other items plugged in to the property. In other words this RCD may fail to operate when other electronic items are plugged in which leak DC in to the mains.
Regulation...
What’s a real life example of an imbalance between live and neutral?
For example, a faulty tumble dryer can trip a RCD on a split board - so I would assume there is an imbalance because of the difference in the magnetic flux between the Live and Neutral coils. But what would be the actual...
DIY question.
I have been changing old metal socket faceplates to the normal plastic ones. All are working fine except the faceplate of a fused switch. Everything works fine when it isn’t screwed. It is a fused spur for a light in the conservatory.
The light works fine when the screws are off...
Hello. we have had a few powercuts over past few months and am in middle of one at the moment where power has gone off a few times while DNO are trying to resolve issue. House is a mid 1980'S PME and on housing estate.
Current setup is single RCD with mcbs. Am currently waiting for spark to...
I've got a dual rcd mk sentry board that I want to inverter into an rcbo board. If I link the two neutral bars from the main switch is this OK to do regs wise? Thanks
Hi, while testing the new board I installed I got to the live testing at the sockets one of the RCD's kept tripping during the loop test, the other ring tested fine so it's not the tester, the insulation tests where all good. Unfortunately I didn't have a residual current clamp meter with me, to...
Had a customer ask for RCD to be changed to Type A as he has had a company install a PV unit which they have left with the spur switched off as new regulations state that PV units must have a type A RCD 🤔. Has anybody else had this situation??
Does anyone have a scheme connecting RCD with UPEU, with details on how wires are connected on reglette and further on UPEU. Can someone explain how alarm is generate when RCD goes down, and where is RCD stationed in rack?
Here is the picture of ports on SLPU:
which should be connected to UPEU...
Evening all,
If a socket circuit is not RCD protected via an RCD/RCBO and there isn't the option of fitting an additional RCD enclosure or fitting RCBOs, is it permitted to add additional sockets to the circuit via RCD spurs or additional RCD socket outlets? (type A of course)...if the sockets...
Hi everyone, each leakage question here.
I am needing to run some LED screens, professional type, not TVs. These are 500mm x 500mm panels and traditionally have 2/3mA leakage per panel.
So we generally have a 63A three phase distro with a 300 mA on input and multiple outputs protected by 30 mA...
I need to replace a Hagar RCD (model number CN284U). This is a type AC RCD and I wish to replace it with a type A.
The model number for the Type A equivalent is CNA584U.
They are both 100mA, 100A, S type.
The only difference being is that the Type A RCD is referred to as 1P + N rather than...
Hi to all. Is there legal requirement for additional dedicated RCD even if we have Double RCD CU?
Our whirlpool bath has ambiguous instructions: first it saying that it has to have separate RCD outside. Then it says "IF separate RCD installed" like if there as an option not installing it.
We...
Best way to add RCD protection to specific circuits in an old Siemens DB which I’m told is now obsolete.
Install an additional enclosure adjacent to the DB to hold new RCBOs and feed these from the obsolete MCBs?
Any other ideas?
Hi,
I’d really appreciate some advice or suggestions as to what could be causing an ongoing issue I have with my RCD tripping.
My RCD trips when I turn my bathroom light off when the boiler is on. It’s worth noting it’s not exactly every time and sometimes when the light has been left on for a...