why am i finding 240v on the neutral ?? we rewired the power in a house and upgraded the consumer unit but when the RCD's are connected they trip different mcb's. when testing we found 240v on the neutral.... when you take away the RCD's everything is fine. we have changed the main switch and...
My confidence levels and ability levels have increased hugely in the past year. In others words I have gone from knowing 0.1% of all there is to know about electrics to around 1.5%!! :)
I would just like to gain more confidence and knowledge regarding ‘tripping RCD’s’!
I have only changed one...
done a small job today. just a socket & SFCU ( for a light) in customer's shed, on existing feed. feed cable is 2.5mm on a 16A MCB, RCD protected. cable tested OK, installed bits. Zs 2.4Ω. ramp test of RCD, mft reads>51mS. prerssed test button on RCD (which the customer said had never been done...
Hello all,
now I know we dont have to retrospectively apply the latest regs to older installations but what is the advice when it comes to doing a periodic on rented accomodation and the consumer unit is quite old and has no RCD's, do you just mark the EICR as N/A or mark it as a fault code...
Hi, anyone got any advice re this problem that I can't solve....
I have 2 PV arrays installed, a 4.2Kw and a 5.0Kw. The electricity supplier here made me install them on 2 seperate single phase supplies. My house now runs on 2 seperate supplies, half on one supply and the other half on the...
Much discussed issue this one. Appreciate any comments.
I let a small one bed flat out. Electric only ie no gas.
Year back I had a new CU put in with all circuits on RCD's (RCBO for lighting). Accompanied by an EICR. Registered ECA sparks did the work.
The EICR documents that the mains...
Hi
I have been asked to put in another socket in a kitchen for a washing machine. Now we are taking 1m of 2.5 clipped in a cupboard however the property does not have any RCD protection. The board is old with them plug in MCB's. Now for reasons to complicated to detail I have no room to...
So...
If you're doing minor works on a lighting circuit (adding/moving lights) and you arn't personally chasing any cables into a wall but you've a sneaking suspicion there may be a few existing switchdrops at <50mm depth....would you insist on RCD protection?
Generally I try and RCD everything...
Hi, My name is Phil and I am based in Warwickshire, whilst I have many years of experience in the electrical industry I have recently come across a problem that I cannot recall seeing before. I installed some new fluorescent fittings in the local community hall and upon carrying out a Zs reading...
Hi guys,
I am helping a friend with extending the ring main and adding some lights etc... in his new bedroom. I have put in a few new sockets & some two way lighting etc... I have isolated the circuits by turning off the appropriate MCB's at the CU which is split and both sides are protected by...
Hello
Just not on the job at the moment but the builder called. He plugged his small angle grinder in to a new circuit and it took out the RCD at the supplying DB not the 30mA at local CU.
Here's the set up:
TT . 100A DNO fuse
House CU old and full so split tails into small CU with...
HI all,
getting some info though that there is problems with Transformer less Inverters and RCD's not tripping.
thought id check one of mine and low and behold it didnt trip.
It is the first time ive tested it with the PV on though so i would never normally pick it up. Looks like the the...
SORRY EXTRA RCD'S :rolleyes2:
Hi guys, i have been reading many other posts but as there are so many well trained sparks on here i thought id put my questions up.
I am having a shower installed in a recently revamped bathroom. Im no expert as you will soon realise but it will be installed by...
i was just wondering where do people buy there s type td rcd's from? there seems alot of different prices on line from 30 pounds to 80 pounds.
i have split load cu with two 63 amp 30ma rcd's on a tt installation, original rcd is 80amp 30ma so trips out when a fault.
could i use 80 amp stype...
Just carried out a periodic on a childrens nursery (built 1994 not tested since), all tested ok but there are no RCD's. Extension leads laying about, radios being taken into the playground etc, what code if any? Be gentle with me it's Monday morning.
Helllo all,
Just a question about the operation of RCD's
At work there is 8 containers all fed from a panel. Each container is assigned a 132A RCD from this panel. The feeder units in each container have RCD's for lights, sockets & heaters ect. When I was fitting some new sockets into one of...
Hi All
I come across a number of cheap RCD's where you can pull the feed wires out (10mm or 16mm - H07VR).
Put the wires back in, tighten the screws so that the heads start to break up, wait a few minutes and you can then wiggle the wires out again.
I think that the problem is that the cable...
Here's the senario. Regency building with 5 flats contained within. System is 3 Phase with a further 2 service fuses added on making 5 in total, earthing is TT. Each flat is fed via a mixture of DP 100mA or 30mA RCD's which in turn feed KMF switched fuse isolators. 16mm T&E tails to each flat...