hi guys just wired up a new ring main for a house, confused on the test results though, firstly all other ring mains in the house that are new are okay and have came out as expected, tester has just been calibrated and batterys are okay and the ring main is a true ring... am using a metrel...
Hi One and All.
Fault finding today. Narrowed it down to one leg of RFC between N&CPC.
What puzzled me was the fluctuation in the IR test. Normally I find the reading stabilises after a short period (5-20 seconds). Today the reading was constantly jumping between 20Mohms with an occasional...
Hi guys, New to testing but been doing installations for about 5 years now. I've come across a problem where the ring I'm testing has no R2 reading, I've split the ring and done a r1+r2 test to find out which leg it's on. Problem is I don't know how the ring was wired. Is there an easy and...
A neighbours underfloor bathroom heating mat stopped working a while back, she asked me to look at it today. Turns out when it was installed the joiner had accidentally burst the cable for it. It's a small thin blue cable that heats up that has two conductors & an earth. Someone has done a...
Hi there
Been stuck on this for a while. What is the maximum r1+r2 reading possible on a lighting circuit in a domestic property. With a type b 6amp breaker.
Also if you guys could tell me about r1+r2 and rn Maximum readings for ring final.
Thanks
On a job today and when testing got a Ze of 0.03 ohms on a tncs. Using a Kewtech 64DL.
Installation has main fuse in hallway outside the 2 bedflat then a switched fuse feeding a submain cable to the actual CU. I did Ze at both immediately before switched fuse and in CU with earth disconnected...
Hello,
I have recently relocated to Slough. Currently looking for Electrical Engineering related job anywhere in Berkshire & London. I am trying hard to get a job but not yet successful. I am wondering if anyone could suggest or recommend me any engineering job. Even I am happy to work as a...
Hi,
Please can anyone advise me as to who would be able to read the internal memory via the IEC 1107 port of an Ampy 5235A meter. I had one installed as a check meter years ago which was left in place & I believe it holds the data I need to claim back from my supplier all unused exported energy...
Afternoon Ladies & Gents,
I'm a new member to the forum so thought I'd introduce myself.
Been qualified for around 10 years and have finally set up on my own. I am new to the test and inspection side of things so I am seeking advise on the following question. Any help would be greatly...
Hi there
Testing at origin of a domestic property, I have found:
L-N: 0.44 Ohms
L-E: 9.89 Ohms
I had the DNO attend clients address, there response was that it was quite high and confirmed readings of 0.44 for ZE. (Pleasee attached document with their response)
My concern is they don't seem...
Electrical Installation Engineers needed to carry out testing and minor remedial works in domestic properties. Vacancies in London, Hertfordshire, Reading and Cambridgeshire on a permanent basis with immediate start available. Engineers must hold their 17th Edition qualification, ECS and...
Hi guys.
I have just tested a ring main. The readings end yo end on the 3 conductors were all fine. When I cross connected the live to neutral and tested around the sockets all of the readings were correct ie R1 + rn÷4. But when I tested with live earth cross conceded the readings got higher...
Been testing a modified circuit today.
Ze = o.20
R1 + R2 = 0.77
Zs = 1.77
So the reading is about 0.80 higher than I was expecting... Nothing on this (lighting) circuit switched on..... I was testing at the end of a smoke alarm addition.
I've read elsewhere, that its a good idea to do a Zs on...
Did an EICR in a domestic property, earthing arrangement was a TN-S with a Ze of 0.51 ohms.
There are 2 ring final circuits protected by 32amp 60898 type B mcbs. Both circuits have additional protection from a 30mA RCD.
My Zs readings for the circuits are 1.63 ohms and 1.89 ohms.
My question...
Evening. Did a Zs test today on a TT lighting circuit and got a reading of 335ohms. I haven't checked Ze yet but I'm presuming that's also in the same ball park. I'm aware of the upper limit Zs of 1667 and the advice contained within the good book that states Zs should be below 200, so I'm in...
I am going to quote for a job (new circuit). Problem is the 10mm water bond is under the living room carpet/furniture as there is no stopcock in the house. I know it's within 600mm of the incoming water pIpe because I connected it there many years ago. I did a quick wander lead test from the...