I would agree with what Murdoch said - Get customer to contact electrician and have him quote BS7671 Reg which is contravened by such an arrangement.
Sounds like a typical EICR comment from a sparkie that comes across something he doesn't normally see then deems it C2 - potentially dangerous, urgent remedial action required!!
Gives us all a bad name, just because it is not how you would do it or what is seen regularly does not necessarily make it potentially dangerous.
I have seen such an arrangement a few times on older installations: 15/16A Radial circuit to 20A DP w/neon "WATER HEATER" switch in kitchen or utility then off to HWC cupboard terminating in a 15A socket with final connection made via 15A plug top and HR flex to immersion heater.
I really don't see a problem with this unless there is evidence of heat damage to connections, installation is in a bathroom (OP indicates this is not the case), the plug is getting used as the method of functional switching or all other sockets in the house are also 15A and the immersion socket is not RCD protected and may reasonably be expected to supply equipment outdoors :wink_smile:
It's not a method I would choose personally but subject to above I can't see the problem. I like final connection via 20A DP switch with flex outlet for 3Kw 240V immersion - 13A FCUs can overheat and burn out when used on constantly used immersion heaters e.g. E7 arrangements.
 
I'm still after advice on the paperwork i would supply to say it's now safe if someone else did the initial test

All you need to do is provide the customer with an invoice detailing the work that you have carried out to rectify the work. They then need to staple that invoice to the original EICR.

If the work warrants a cert, that covers it too
 
I just did a quick bit of mental arithmetic as in 3000 div 230 and then 240!! hey presto 13 and 12.5!! ...lol!! Youre problem is, that you're using a make believe nominal voltage, rather than the real voltage!!

"Your problem is" that you're forgetting which part of the power calculation in this instance is constant. The resistance, apart from a slight variation through increased conductor/element temperature is the constant. The power is not constant at all.

If you introduce a greater potential difference across this fixed resistance you get an increased flow of current, with increased current you get a hotter element as well as a higher power consumption.

This is electricity 101.
 
All you need to do is provide the customer with an invoice detailing the work that you have carried out to rectify the work. They then need to staple that invoice to the original EICR.

If the work warrants a cert, that covers it too

ok, thanks. so the fact that on the report the installation is rated as unsatisfactory is not a problem as long as the invoice states that the faults are now resolved?
 
I think all the calculations going on have veered from the initial question of whether a 15A plug and socket need to be changed and warrent a c2.what about the rule that if it previously complied, it's not necessarily unsafe.and on that subject, unless you've been an electrician since the first edition, how would you know if something was permitted before?
 
554.3.3 prohibits the use of a plug and socket to connect water heaters having immersed and uninsulated elements. This often causes confusion as some take this reg to apply to normal domestic elements. It applies only to a type of element I have never come across.
It is possible that the C2 has been applied based on this reg.
 
Deleted
 
Last edited:
I think all the calculations going on have veered from the initial question of whether a 15A plug and socket need to be changed and warrent a c2.what about the rule that if it previously complied, it's not necessarily unsafe.and on that subject, unless you've been an electrician since the first edition, how would you know if something was permitted before?




May I ask what 15A plugs are for?
 
554.3.3 prohibits the use of a plug and socket to connect water heaters having immersed and uninsulated elements. This often causes confusion as some take this reg to apply to normal domestic elements. It applies only to a type of element I have never come across.
It is possible that the C2 has been applied based on this reg.

It also may have failed due to the 553.1 group of regs, mainly 553.1.100 where every socket outlet for domestic use shall be of the shuttered type and for AC use preferably of a type complying with BS1363.

553.1.3 and 553.1.5 seem to contradict 551.1.100 somewhat, in that table 55.1 implies that a 15A BS 546 S/O is acceptable.

As to C2, is it a bit harsh ?, would a C3 been a fair call ?, I suppose it is down to the spark on the ground on the day.
 
554.3.3 prohibits the use of a plug and socket to connect water heaters having immersed and uninsulated elements. This often causes confusion as some take this reg to apply to normal domestic elements. It applies only to a type of element I have never come across.
It is possible that the C2 has been applied based on this reg.
That reg would be a bit ambiguous to me. I'd class a standard domestic tube element as being insulated, it is earthed after all. An uninsulated element to me would mean an electrode type boiler where AC power isapplied directly to the immersed plates and the load current actually flows through the water being heated but I've never seen these in a domestic application, only in industrial steam generators. If the reg refers to an electrode heater though why doesn't it refer to them by name?
 
"Your problem is" that you're forgetting which part of the power calculation in this instance is constant. The resistance, apart from a slight variation through increased conductor/element temperature is the constant. The power is not constant at all.

If you introduce a greater potential difference across this fixed resistance you get an increased flow of current, with increased current you get a hotter element as well as a higher power consumption.

This is electricity 101.


I'm doing nothing of the sort, the fact is, you're all applying 230V criteria to a power system that has a nominal voltage of 240 volts!! As i said earlier, 230volts is all make believe ...or a fairly tale if you like!! lol!!
 
554.3.3 prohibits the use of a plug and socket to connect water heaters having immersed and uninsulated elements. This often causes confusion as some take this reg to apply to normal domestic elements. It applies only to a type of element I have never come across.
It is possible that the C2 has been applied based on this reg.

but the regs are for new installations, not to bring every old installation up to the current regs, so why would a plug and socket fail anymore than having re-wirable fuses, for example?
 
but the regs are for new installations, not to bring every old installation up to the current regs, so why would a plug and socket fail anymore than having re-wirable fuses, for example?

Un-shrouded pins possibly ?, or as another poster said a misunderstanding ?, the point is, if the inspecting spark is unhappy with something then he should have put the reg it contravenes in the report, personal preference does not come into it, C2 may have been a bit harsh, but without knowing the reasoning behind it we cannot criticize.
 

Reply to 15Amp immersion plug in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
380
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
956
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Article
This is an RSS feed of thread: Two electrical supplies and a single immersion element Content of the thread: Good afternoon, new joiner here with...
Replies
0
Views
197
I think it is a good idea in general, it provides a form of proof that the landlord has provide access to the required documents. further to that...
2
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top