OP
Baal
IR testing can be done on individual circuits once the installation is re-energised-they're trying to get you to list JUST the tests that require the installation to be isolated.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss 2391 exam question in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
IR testing can be done on individual circuits once the installation is re-energised-they're trying to get you to list JUST the tests that require the installation to be isolated.
Like I said earlier, I don't think I'd like to be poking around inside an energised CU doing a dead test.
I'm pretty sure it also contravenes the EAWR.
Work on or near live conductors
14. No person shall be engaged in any work activity on or so near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless–
(a)it is unreasonable in all the circumstances for it to be dead; and
(b)it is reasonable in all the circumstances for him to be at work on or near it while it is live; and
(c)suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.
hi baalI agree with the EAWR comment but then you wouldn't be able to carry out a loop test or a phase sequence test etc as shown in guidance note 3.
The examiners report criticised candidates for merely listing the dead tests as an answer to this question, implying that IR would be the only dead test not carried out during the isolation.
. .Yes, there are 3 tests here that require the isolation of the installation:
Continuity of protective bonding conductors
External earth fault loop impedance
Prospective fault current Why do you need it isolated for this test?
Don't write 'Ze' and 'PFC' etc-this exam is marked on correct terminology and the examiner will want to see the correct names for the tests.
Also, what about the neutral/earth 'link' - that's gonna throw your results on individual circuits.....or are you talking about disconnecting circuits from the board now to perform the test.
Hope you disconnect the correct neutral, then.
In my opinion, you do a 'full installation' IR test whilst it's isolated
wheres the clue i was told of chief tutor at bury college that as it states list and gives 6 marks then they are looking forHi Bruce
You have 60 minutes to carry out all of the above tests, they are giving you a clue so the answer is i) iv) and v)
The examiners report criticised students for merely listing all of the dead testing as this would not be possible given the time constraints.