What local distribution network, all of these things can be found on a small domestic install these days, I'm not going to back down and no one has yet given proof that the N cannot be overloaded in the scenario given by the OP.
So until this is done I stand by my arguments, I DESIGN, I DO NOT GUESS values, so the N can be overloaded, & if I was being paid for my consultancy then I would be bothered to calculate things, as I am not, it;s down to you lot to prove otherwise, which, as yet, you have failed to do.
Ok I may have missed some thing here, say you have a tp&n supply connected to a switch fuse with say a 4 core swa feeding a tp&n db and all loads on that db are single phase, would that be incorrect? Would you oversize your neutral?
No it's not a tp+n supply & it's not to a db, it 3 off final circuits fed from the same 3p mcb, with a common N to all circuits, and the cct's are socket outlet circuits.
I never said never, I just said given the OP, it was highly unlikely.
On another note, PF is not cumulative in the sense that if a system is made up of loads at a PF of .9, the overall PF is still .9. The average domestic install is expected to average out at roughly .9 - .95, three of those domestic installs across three phases and the slightly negative effects caused by the non-linear loads within each dwelling become meaningless. The exact reason for this can be found within our discussion regarding our three 20A socket circuits.
We all suffer from a lack of understanding at times (myself included! :D) you have since seen sense but still seem to be fixated on being theoretically correct. It seems to me that you're just not looking at the bigger picture.
I am not talking about PF, I am mainly talking about distortion of the supply, I have never said anything about PF.
Supply distortion these days has a much bigger affect on installs than PF as this is normally taken care of, but, distortion IS cumulative.
Fantastic thread guys.............well done to all.
Great stuff:)
Hahaha...must have a proper read tomorrow!
The original Q just appears to be an unbalanced Star with a Neutral, what's the problem?!?! :sifone::smilielol5:
If you sort it out let me know mate.................I've agreed with at least 10 differing versions up till now lol
TO be honest, whist there seems to be a lack of belief from posters here with regard to what I am saying, there seems to be a significant lack of understanding of what I am trying to put across as well, I don;t know how else to describe things.
Thing is see, I'm not a spark, I operate mostly as an Engineer, & consultant thus I am paid for my opinions, & I don't start throwing arguments about unless I can back them up, because that is how I make my living, and I'm doing OK, thank you and have been for a few years now, based solely on my own personal opinion, which is hen backed up by fact once the money starts flowing, why should I do otherwise when it is my living.
I'm not proposing anything as stupid as payment here, I'm here for the fun of it. but, I will never post anything that I cannot back up, and no one has managed to prove with science that my arguments are incorrect yet, once they do I will give an apology, until then I stand by them.
In the OP, the N conductor CAN be overloaded.
The circuit is not acceptable.
If anyone can PROVE otherwise in all scenarios then I will bow down, until then I await proof.
3 sp circuits off a tp isolator
Electrical Wiring, Theories and Regulations
Tidy Max,
Dan,