63 Amp Isolator | Page 2 | on ElectriciansForums
Discuss 63 Amp Isolator in the UK Electrical Forum area at ElectriciansForums.net
Surrey
I'm running a 63A supply for a cooker and need to have a local isolator.
Apart from having a 63A main switch in a small enclosure, is there any thing else I could use which is discreet to put in the back of a cupboard.
which doesn't necessarily prevent a N-E fault tripping the RCD.
You're quite right, it doesn't. But then a N-E fault could occur on any circuit at any point. Should we have local isolation at every point of utilisation, and then local isolation protecting each point of local isolation??
Best practice or personal opinions aside. A cooker does NOT 'need' local isolation. In fact, find the words 'local' and 'isolation' next to each other in the BGB and I'd be flabbergasted!
537.2.1.2 can be met by the MCB. It could NOT be met by using a cooker control unit, so that one is irrelevant.
537.3.1.2 can be met by the use of a locking off device.
Try again.
had a feeling you'd come back with that plus I just read on next page it saying a mcb can be used as a isolator.
god damn it i was taking everyone down the pub.
any way the thread has been hijacked some what, what about the isolator weather you use one or not cos i do
Good practice says to me that every fixed appliance that can not be DP isolated by pulling out a plug (and not having to move an appliance) should have a DP isolator.
If you must persist with your it doesn't need a isolator I would concede ONLY IF the cooker was on a dedicated RCBO
Reply to 63 Amp Isolator in the UK Electrical Forum area at ElectriciansForums.net
I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...