I'm running a 63A supply for a cooker and need to have a local isolator.
Apart from having a 63A main switch in a small enclosure, is there any thing else I could use which is discreet to put in the back of a cupboard.

Thanks
 
which doesn't necessarily prevent a N-E fault tripping the RCD.

You're quite right, it doesn't. But then a N-E fault could occur on any circuit at any point. Should we have local isolation at every point of utilisation, and then local isolation protecting each point of local isolation??

Best practice or personal opinions aside. A cooker does NOT 'need' local isolation. In fact, find the words 'local' and 'isolation' next to each other in the BGB and I'd be flabbergasted!
 
537.2.1.2 can be met by the MCB. It could NOT be met by using a cooker control unit, so that one is irrelevant.

537.3.1.2 can be met by the use of a locking off device.

Try again.

had a feeling you'd come back with that plus I just read on next page it saying a mcb can be used as a isolator.
god damn it i was taking everyone down the pub.

any way the thread has been hijacked some what, what about the isolator weather you use one or not cos i do
 
You're quite right, it doesn't. But then a N-E fault could occur on any circuit at any point. Should we have local isolation at every point of utilisation, and then local isolation protecting each point of local isolation??

Best practice or personal opinions aside. A cooker does NOT 'need' local isolation. In fact, find the words 'local' and 'isolation' next to each other in the BGB and I'd be flabbergasted!

Good practice says to me that every fixed appliance that can not be DP isolated by pulling out a plug (and not having to move an appliance) should have a DP isolator.

If you must persist with your it doesn't need a isolator I would concede ONLY IF the cooker was on a dedicated RCBO
 

Reply to 63 Amp Isolator in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
181
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
556
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
516

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
469
  • Question
If it's buried ducting, have you thought about digging up a section of the buried cable close by, cutting it and pulling in a few extra meters...
Replies
6
Views
784

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top