A good guide For 'exported PME' and outbuildings!
For anyone bored by the constant myths and rumours regarding this subject, have a read of this guide from the IEE on supplies to detached outbuildings.
It was published in 2005 but the important bits remain unchanged and might be of some help!
Thanks IQ. But what if user is wearing wellies and there's no RCD protection in garage (but is in house). User is holding failed tool and therefore a live part, hasn't got a shock because there's no earth path but then touches water pipe on side of garage. Will MCB or RCD in the consumer unit in the house provide any protection? If no, then shouldn't earthing be improved in the garage (e.g. bonding of this pipe and either TT or 10mm2 back to consumer unit). Thanks, SW.
If there's RCD protection in the house and the garage is fed from the house...then the garage will be RCD protected.....it doesnt matter how far back up the system the rcd is...the current imbalance it see's will be the same.
:wink5:
An important omission is the fixing height of a socket outlet in a garage.
The 17th Edition of the IEE Regs require it to be fixed at a suitable height.
The 13 Edition stated a height of 4ft 6 inches. (1.5 metres)
This was to try to remove the risk of explosion / fire from petrol fumes.
This is a good guide line for today's installers
Hi just a reply to the Thought that Neutral breakdowns in PME supplys are Rare,, Last week I was called to a house that had been recently rewired by another party and then tenants moved in..
Dueing the day they were shocked to see smoke from under kitchen sink. the flexy hose had melted and blown apart leaking water across the kitchen a plumber came out to fix it and got a shock everytime he tryed to reconect it, an electrician was called but couldnt find the problem!!
i was called and found a high resistance on the neutral supply and when the kettle was put on and the shower run (any high load) The main and supplementary bonding became the prefered return path!!! just a thought when running to external systems garages etc.. a nice metal framed garrage would make a lovley return path!!... also note this was a 17th edition board so completly RCD protected the RCD was never unbalanced because the fault was external of the RCD
Good guide indeed!
[TABLE="width: 445"]
[TR]
[TD]Electrician Brisbane south west Jindalee[/TD]
[/TR]
[TR]
[TD]www.ecoelectric.com.au
[/TD]
[/TR]
[/TABLE]
[TR]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[/TR]
[/TABLE]
[TR]
[TD][/TD]
[/TR]
[TR]
[TD][/TD]
[/TR]
[/TABLE]
This subject has been done to death over on the S/F Sparks Forum.
A few years ago I posted what I called tongue in cheek thread about 'The Utimate PME/TNS Exportation'
The following is a Cut & Paste from said thread with suitable updates for the current Regs.
The Ultimate PME/TNS Exportation! by Sinewave.
Existing
PME/TNS supply at service position.
Run a minimum of 10mm 3 core SWA cable to your external location, following all approved cable installation
procedures.
Terminate in to a 17th Ed Metal Clad Dis-Brd or use RCBO's for all Circs depending on size of remote installation.
Link SWA Earthing Tag to DB-2's MET with 10mm, despite it being a Metal Clad Dis-Brd.
(Belts & Braces!)
Drop an Earth Rod in as close as possible to DB-2 and connect back to DB-2's MET with 10mm
Bond any metal services entering
the remote building with 10mm
Bond any exposed metal framework of the
building with 10mm
Resultant installation has an excellent Ze DB-2
Resultant installation is tied down to 'True Earth' at it's remote
location thus avoiding any 'potential' differentiation problems between the MET at the DNO service poistion/DB-1 and the remote installation at DB-2.
Most of the UK's MV Network is PME'd now lead or otherwise as all joints have a Rod dropped in as a matter of course.
I noticed the other day, a post on the IET's forum linking to this sticky, which made me chuckle as the link here is to a guide on the IET's website.
The way i look at is, if i export PME am i taking it into a zone where an equal potential can be created. If it can then there's no more of a risk than anywhere else.
Personally if i cant create an equipotential zone i wont export, or ill go done the route of placing an electrode system of a suitable Ra to keep the touch voltage down.
With the country now becoming pretty much PME it will be interesting to see the rate of failures on the network to see how rare these broken pens are now.
Regards Chris
Regards Chris
And that's what it all boils down to....
Regards Chris
Why not take the PME to the outbuilding/shed or whatever, and connect a rod to the EMT at the small CU?? You then have best of both worlds relatively speaking. Personally i wouldn't feel the need to rod, i'd be more than happy with the PME...
The way things are in modern times, is profits Rule!!! and it's how much that maintaining PME is going to eat into those profits that will decide. That and substantial fines and/or damages for Not maintaining their LV network earthing systems...