Can’t see that happening in a kitchen where there is an American FF though!
Could bounce off of the other thread with the SWA going outside the house and then back in to an outlet!
No he is right , as long as the circuit does not require an RCD because of installation methods.
I was going to suggest that if it was only high earth leakage that is causing the problem
RCDs are required for...
1. Sockets.
2. luminaires.
3. cables buried <50mm deep in walls ( unless otherwise protected yadayada.
avoid 1.2.and 3, by 1.fitting FCU instead of socket, 2 is irrelevant. 3.choosing installation method .
The requirement is for socket outlets and installation methods . As long as your method does not require rcd protection and you are sure the FF is not faulty there is nothing to stop you using an fcu as @telectrix suggests.
If it is a posh kitchen it will probably cost as much to put in than to fix the thing. ;)
PS . It will depend on your board , you may not have an unprotected way . It might start getting ...
Or > 50mm lol. Might be lucky and have a wooden floor or cellar. ;)
Not be pretty . Engineer is the best option
True but i meant with minimal disruption lol if its an all singing all dancing kitchen i seriously doubt theyd want any chasing to be done let alone that far into a wall and they wouldnt want trunking or conduit
As others have said the best option is to get it fixed, if it's less than six years old (five years in Scotland) they could claim against the supplier, it's unlikely that anything other than a manufacturing defect would cause intermittent RCD trips in a new-ish product.
If all else fails it could be powered from an isolating transformer, fridge-freezers don't take much peak power so a transformer wouldn't be a silly size or cost. It would be a bit of a hack but so long as the earth bond is maintained it would be safe and would prevent RCD trips.
Does it record the info or do you have to watch it and wait for the moment it trips?
It will record either min or max for as long as the supply is on.
When supply is off(trips) it stops recording data but will leave you with a reading.
I have a mock up adaptor I use to separate L N E in the appliance flex as clamping the flex as a whole will give no reading.
I was without one until a year ago it really does save alot of agro.
Reply to American FF tripping RCD in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Which rcd is it? Is it one for everything, one for a few circuits?
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
davesparks