D
Deleted member 26818
Can't be asked.
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss another 2391 question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Try Regs 522.6.101, 522.6.102 & 522.6.103 in the BGB.Sorry, could you please furnish us with the number of the Regulation that requires Circuits that supply socket-outlets to have RCD protection?
Exactly, a condition where the additional protection is required, and no exceptions are allowed.The question in the OP asks for one condition where BS7671 requires additional protection by an RCD, NOT for exceptions.
JUD the those Regulations do not refer to or even mention circuits. They refer to cables.
Also in those Regulations, RCD protection is not a Requirement, just an option.
As I have said now on a number of occasions, the only place where you will find requirements for RCD protection for circuits, is in Chapter 7.
Exactly, a condition where the additional protection is required, and no exceptions are allowed.
If the question asked for one condition where 30mA RCD protection is required for socket-outlets in an office, the answers would be where the socket-outlets are intended to be used by ordinary persons, or are used to supply mobile equipment outdoors.
If the question asked for one condition where 30mA RCD protection is required for cables concealed in walls of an office, the answer would be where the cable is at a depth less than 50mm, does not have an earthed metallic sheath, is not in earthed conduit or trunking, does not have mechanical protection sufficient to prevent penetration by screws or nails and the office is not under the supervision of a skilled or instructed person.
i.e. a home office, or an office in a domestic installation.
If the question asked for one condition where a circuit requires 30mA RCD protection, one answer would be when the circuit is of a location containing a bath or shower.
As it's unlikely that an office will have a bathroom or shower-room, and even if the office did, as the building is six years old, the bath or shower room, would not have socket-outlets, as the Regulation allowing socket-outlets in such locations, did not exist six years ago.
The question asks for one condition where irrespective of the installation method for the cables, irrespective of the use the sockets are intended for, irrespective of whether there is supervison by a skilled or instructed person, a condition where in every instance, the circuit will require 30mA RCD protection.
There is only one condition that would in every instance require an office circuit that supplies socket-outlets to be provided with 30mA RCD protection, and that is when the office is part of an Agricultural/Horticultural installation.
A very well thought out and thourough argument, except that the question relates to circuits, not to items of equipement that are just a part of a circuit.
Iagree, that the question does not specify what it supplies, however it does specify that 30mA RCD protection is required.
Circuits that supply socket-outlets in Agricultural/Horticultural installations in all instances require 30mA RCD protection. No exceptions.
Typical IET questions, cryptic, designed to confuse and trip you up. With several possible answers depending upon how you interpret it, just like the regs themselves. Enjoyed the debate though.
Think i need to do the 17th. No RCD protection on a TT system?
Is that what spinlondon is saying or have i missed the question?
Reply to another 2391 question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net