Bring back the old Category 1 to 4 system I say as Code 1 and 2 are far too similar in meaning. Is a missing blank a Code 1 (Danger present) or Code 2 (Potentially dangerous). A blank missing is a potential danger in my eyes as there is potential to cause harm. What does danger present represent exactly.
 
A Code 1 (C1) observation means ‘Danger present, risk of injury, Immediate remedial action required.’ It is an immediate threat and should be rectified or made safe as soon as possible. An example of a C1 defect would be accessible live conductors due to damage, poorly modified enclosures or removed maintenance panels. Incorrect polarity would also attract a code C1 as it may allow conductive parts, not normally expected to be live, to become live.

The presence of a code C1 warrants immediate action to be taken which would be to inform the duty holder or responsible person for the installation immediately, both verbally and in writing, of the risk of injury that exists.

A Code 2 (C2) is a potentially dangerous defect, these might be things that don’t pose an immediate threat but are likely to become a danger in the future. A C2 is described as ‘Potentially dangerous – urgent remedial action required.’

The phrase “potentially dangerous”, in the C2 code is designed to point towards a risk of injury from contact with live parts after a sequence of events. A sequence of events could mean that an individual may gain access to live parts through a day to day task that would not be expected to give access to live parts.

An observation code FI is described as ‘Further investigation required without delay.’ This means that your electrical contractor has observed something whilst carrying out the testing for instance emergency lights seem very dim. This might not have been covered in the report so they have noted it separately as code FI.

Codes C1 and C2 attract unsatisfactory report findings and you’ll have to have these defects rectified in order to prove compliance. A report could also be classed as unsatisfactory if the only fault codes are FI. An example would be when there are lots of circuits that are not verified at the time of testing, this is because the inspector would not be able to categorically say that these circuits are safe or not.

Code 3 is described as ‘Improvement recommended.’ This means it does not comply with the regulations but isn’t actually dangerous. A code C3 should imply that the installation is not necessarily dangerous but it may not comply with the current version of the regulations or for example, may have damaged fittings that do not have exposed live parts. A code C3, in itself, should not warrant an overall unsatisfactory report.

You will need to address C1, C2 and FI faults on your report in order to achieve compliance. Once faults have been rectified and your electrician has issued you with the relevant paperwork, Electrical Installation Certificate (EIC) or Minor Works Certificate (MW) these should be kept together with the EICR to prove all faults have been rectified in accordance with BS7671.
 
I personally think every scenario is different.
Accessibility comes into it in my opinion.
For instance today I had a fused spur in the loft area supplying the tv amplifier for a small block of flats , cover not screwed back so exposed live parts.
Normally I would c1 this however the loft area is only accessible by step ladders ( non fitted internally) and the loft cover can only be opened by a hex key.
I did not c1 this in this scenario.
 
If there is blanks missing from a CU what code would this be.
Scenario 1 .. 6 blanks missing from a CU in a corridor cupboard
Scenario 2 8 blanks missing from a locked corridor cupboard

Looking at 3 diffrent reports they have same faults but have been coded differently.

If the report(s) contained any C1's, shouldn't they have had the necessary remedial action taken immediately?
 
I personally think every scenario is different.
Accessibility comes into it in my opinion.
For instance today I had a fused spur in the loft area supplying the tv amplifier for a small block of flats , cover not screwed back so exposed live parts.
Normally I would c1 this however the loft area is only accessible by step ladders ( non fitted internally) and the loft cover can only be opened by a hex key.
I did not c1 this in this scenario.
Risk assessment, method statement...…..and screw the cover back....? ;)
 
I personally think every scenario is different.
Accessibility comes into it in my opinion.
For instance today I had a fused spur in the loft area supplying the tv amplifier for a small block of flats , cover not screwed back so exposed live parts.
Normally I would c1 this however the loft area is only accessible by step ladders ( non fitted internally) and the loft cover can only be opened by a hex key.
I did not c1 this in this scenario.
I would have screwed it back on.
 

Reply to Blanks missing from CU in 2 senarios in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
There is no homework, and I'll never see these photo again.
Replies
3
Views
623
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
348

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top