Looking for some guidance please.
Lived in current house just over a year now and had couple issues with our pull cord switch (45A) sticking. Also at its worst, experienced the neutral burnt out.
My relative (industrial electrician) has put some potential issues across to me so was hoping you could all help make sense of it all.
Shower is 9.5KW
Unsure on voltage 230/240
Cable is 6mm
MCB is 32A type 2.
Cable from consumer to pull cord no more than 10M inside wall.
Pull cord to shower 1-2M above ceiling.
They have put doubts to me that the cable may not be big enough
Other option is they said to get smaller shower.
Looking for some guidance please.