Wouldnt the size of cable installed depend on what size switch-fuse is fitted, which depends on the size of the DNO fuse?
No - select the cable size required to supply the CU, then fuse accordingly. DNO fuse does not come in to the equation - that's the whole point of putting in a switch fuse.
I might be reading this wrong, but are you saying that you are allowed to fit a 100A switch-fuse even though the DNO fuse is only 80A? Dont you use discrimination when using fuses? So if the DNO fuse is 80A then the switch fuse has to be smaller?
Now on site and route for cable is straight run 12m accross new concrete floor (not yet laid) to csu up walls either end. metal switch fuse no rcd to be put in cabinet, 16 or 25.mm swa to run to existing plastic csu. if 25mm would be 2 core with seperate 16mm earth. wanting to know best method to run in or under floor.
In hardcore below, or in the 4 inch of insulation, or in screed. All should be easy if i get in first.
2/ ...Run either SWA or conduit/duct in the slab using any re-bar steelwork to fix
5/ ...If using SWA then go with 25mm, at least you'll cover any future upgrades...
I assume your talking standard pvc tails and not swa. what conduit would be best for swa.Tails will need fusing down as they enter, via a switched fused spur. Then flexible ducting can be used for beneath the concrete. Also an RCD would be ideal as they are not in steel conduit or anything similar.