Calculating volt drop, cable selection and mcb selection on an 3kw motor

ok here i go :

For deign current : 36.1 A

In : 40A
...................

Ok..... here goes...

Ca : 35 oc...... : factor of 0.94....table 4b1 ?
Cg : 0.82........table 4C1 ???

so ...It = 50.8 A ...????

Im lost as to where i go from here....

I can do the volt drop calc....but i cant suss how to find the correct table for the cable selection ?

Thanks
 
how do you get 36.1A for a 3kw motor?
 
Ib -

Ib = Power / SQUARE ROOT of three x Uo = 36.1 A

In = Greater than Ib = 40A breaker

It : = In / Cg = 40 / 0.82 (table 4c1) ......It = 48.78 A

(these values have changed)

Cable : 4mm cable (Table 4G1A , column 9) ?????????????????
 