I want to give you one last question on cable selection (to allow for 400V) then we can do some maximum demand/diversity and adiabatics (sizing of protective conductor) :p

4.

A 25kW, 400 V three-phase heater is wired in thermoplastic sheathed MICC cable fixed to horizontal perforated cable tray. The circuit is run with two other circuits and the maximum permitted volt drop is 6 V. The length of run is 28m and the heater is protected by a BS EN 60898 Type B triple pole circuit-breaker. The ambient temperature is 35 degrees C.

i) Design current
ii) Rating of protective device
iii) Current-carrying capacity of the cable
iv) Volt drop within the cable
 
Spot on




Selecting cable too soon.. will waste time in your exam :)



You've selected the correct factors etc, so if you put these workings down you would get a good quantity of the mark. However one thing you need to consider is the potential of overload.
The question reads 'heating load', not 'load' or 'sockets'. Because of this we can assume that the heater is of a fixed rating and so overload won't occur.
This therefore means that instead of using (In) divided by the correction factors, we could instead use (Ib).
It also means that the Cc factor of 0.725 (due to the BS3036 fuse) can also be omitted from the formula.

So the formula can be put down as:

It= Ib/(CaxCg)

= 13A/(0.80x1.03) = 15.7A

So from table 4D2A Column 6 we can pick a tabulated current-carrying capacity = 1.5mm carries 19.5A
Much respect to you Widdler for putting so much time and effort in. One very small point which doesn't affect the outcome at all. The question said
buried within the building material of the installation
So wouldn't that mean ref method B [42 from table 4A2?] not ref method C, so table 4D2A column 4 = 1.5mm² carries 16.5A

or am i wrong ?:)
 
Last edited by a moderator:
how the hell do i find a list of cb's/ select them from the OSG ????????? ...or have i just overworked my brain ????????? lol


Off the top of my head i don't think there is a list in the OSG - i always use appendix 3 of BS7671.

edit - oops table 7.1 seems to show them
 
Last edited by a moderator:
that q has really baffled me....Is the MCB ratings differnet when talking about 400v/ triple pole ? if so how do i find out which type to use and therefore do the resulting equations become affected ?
 
Much respect to you Widdler for putting so much time and effort in. One very small point which doesn't affect the outcome at all. The question said
So wouldn't that mean ref method B [42 from table 4A2?] not ref method C, so table 4D2A column 4 = 1.5mm² carries 16.5A

or am i wrong ?:)

Selected reference method was C (No. 57).

In questions where it states within building materials, it refers to direct in masonry. :)
It's all down to interpretation of reference methods, the syllabus I use have in this example gone with the above. But your opinion of reference method B can also be justified.
It's one of the biggest debates I have with my guys.
 
that q has really baffled me....Is the MCB ratings differnet when talking about 400v/ triple pole ? if so how do i find out which type to use and therefore do the resulting equations become affected ?

The question is answered with the exact same approach and formula bar one. The design current (Ib).

With Three phase (400V), we use the following formula:

Ib =
Power (P)
√3xUL
 
Selected reference method was C (No. 57).

In questions where it states within building materials, it refers to direct in masonry. :)
It's all down to interpretation of reference methods, the syllabus I use have in this example gone with the above. But your opinion of reference method B can also be justified.
It's one of the biggest debates I have with my guys.

Cheers for the reply, on reflection 57 is probs a better fit :)

I suppose we all have to carry our thermal resistivity meter in our kit as well ;)

Thanks for keeping my brain ticking over!
 
The question is answered with the exact same approach and formula bar one. The design current (Ib).

With Three phase (400V), we use the following formula:



Ib =
Power (P)



√3xUL
[ElectriciansForums.net] Calculating volt drop, cable selection and mcb selection on an 3kw motor


Not sure what other posters think but Widdler deserves that for this thread, it was good of you to help that lad out the way you did. Top man
 

Reply to Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
307
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
828
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
924

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top