...success....!!! good tutor you see ;-)
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss Calculating volt drop, cable selection and mcb selection on an 3kw motor in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
now thats thrown me....Do i consider the cable to be in insulation ?
Do i need to confirm the protective device rating if it is given ? (check it maybe ? )
Spot on
Selecting cable too soon.. will waste time in your exam
You've selected the correct factors etc, so if you put these workings down you would get a good quantity of the mark. However one thing you need to consider is the potential of overload.
The question reads 'heating load', not 'load' or 'sockets'. Because of this we can assume that the heater is of a fixed rating and so overload won't occur.
This therefore means that instead of using (In) divided by the correction factors, we could instead use (Ib).
It also means that the Cc factor of 0.725 (due to the BS3036 fuse) can also be omitted from the formula.
So the formula can be put down as:
It= Ib/(CaxCg)
= 13A/(0.80x1.03) = 15.7A
So from table 4D2A Column 6 we can pick a tabulated current-carrying capacity = 1.5mm carries 19.5AMuch respect to you Widdler for putting so much time and effort in. One very small point which doesn't affect the outcome at all. The question said
So wouldn't that mean ref method B [42 from table 4A2?] not ref method C, so table 4D2A column 4 = 1.5mm² carries 16.5Aburied within the building material of the installation
or am i wrong ?
how the hell do i find a list of cb's/ select them from the OSG ????????? ...or have i just overworked my brain ????????? lol
Much respect to you Widdler for putting so much time and effort in. One very small point which doesn't affect the outcome at all. The question said
So wouldn't that mean ref method B [42 from table 4A2?] not ref method C, so table 4D2A column 4 = 1.5mm² carries 16.5A
or am i wrong ?
Selected reference method was C (No. 57).
In questions where it states within building materials, it refers to direct in masonry.
It's all down to interpretation of reference methods, the syllabus I use have in this example gone with the above. But your opinion of reference method B can also be justified.
It's one of the biggest debates I have with my guys.
that q has really baffled me....Is the MCB ratings differnet when talking about 400v/ triple pole ? if so how do i find out which type to use and therefore do the resulting equations become affected ?
Selected reference method was C (No. 57).
In questions where it states within building materials, it refers to direct in masonry.
It's all down to interpretation of reference methods, the syllabus I use have in this example gone with the above. But your opinion of reference method B can also be justified.
It's one of the biggest debates I have with my guys.
Cheers for the reply, on reflection 57 is probs a better fit
I suppose we all have to carry our thermal resistivity meter in our kit as well
Thanks for keeping my brain ticking over!
The question is answered with the exact same approach and formula bar one. The design current (Ib).
With Three phase (400V), we use the following formula:
Ib =Power (P)
√3xUL
Not sure what other posters think but Widdler deserves that for this thread, it was good of you to help that lad out the way you did. Top man
Not sure what other posters think but Widdler deserves that for this thread, it was good of you to help that lad out the way you did. Top man