Evening chaps..

I have just fitted some downlights in a bathroom and needed to give them RCD protection as there was none. I fitted the following:

[ElectriciansForums.net] Cannot get RCD test to work?

The test button works fine and the unit trips when a fault occurs (touching neutral to earth) but I cannot get the MFT to test it for trip times which I need for the MWC. Its a fairy decent MFT and I've never had any trouble with it testing RCD's before but I have never tested this sort of RCD before, it has always been in the CU. I make contact with the live/neutral/earth of something which the RCD is feeding, I get the little 'tick' on the MFT and then it just wont test.

Am I missing something simple here? Is this unit tested in the same way as you would an RCD in a CU?
 
Well you haven't done that to me so don't worry about it MM, it was nothing but a discussion from where I was sitting.
Enjoy the Moto GP, is Valentino Rossi still riding? Obviously you can see that I know three tenths of bugger all about it but my brother rates him very highly.
 
Was IR testing carried out through this RCD?

Glenn!! You're going to have to go back through the thread!! I did all tests and gave all results... Zs, IR, Continuity of CPC, pi R sqared, E=MCsquared and the meaning of life are all in this thread somewhere... Just look!! ;)
 
Glenn!! You're going to have to go back through the thread!! I did all tests and gave all results... Zs, IR, Continuity of CPC, pi R sqared, E=MCsquared and the meaning of life are all in this thread somewhere... Just look!! ;)

Do I remember rightly that RCD testers abort the test if the voltages induced by the test (relative to the CPC) are too high?
 
I know it sounds rediculous but make sure you have a good connection where you are testing, I have found that if testing an rcd, say at a light fitting, it can make it not work properly if you arenot holding the probes on tight enough. Just a though....

Oh and make sure you have your leads plugged in the right holes on your meter, I did that once, can't remember which was round they were but it wouldn't trip the rcd as much as I tried.
 
Well you haven't done that to me so don't worry about it MM, it was nothing but a discussion from where I was sitting.
Enjoy the Moto GP, is Valentino Rossi still riding? Obviously you can see that I know three tenths of bugger all about it but my brother rates him very highly.
Marquez is the boy at the moment. Rossi still in there, even Edwards and Hayden still going.
 
Thought RCDs were good for 500V apart from RCBOs on which you have to remember to disconnect any functional earth? If the RCD has been killed, wouldn't that result in a failed test rather than refusal to test?
may just not test at all....

personally i think theres either a lack of understanding about how to carry out the test competantly from the OP (hardly surprising)

or theres no continuity of CPC someware......

if theres any exposed pipework nearby the OP could prove the no continuity of CPC easily by connecting the earth croc to extranious whilst testing the RCD.....if it lets go then i would dare say its a CPC thing....
 
Try testing live (load side) to earth only(neutral and earth probes)
Did an rcd spur work out cheaper than fitting an rcbo at the board?and where did you site it?Above the ceiling?
 

Reply to Cannot get RCD test to work? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
865

Similar threads

Ok I’ll try this when I’m down
Replies
4
Views
387
L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
657

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top