As above, came to commission a circuit yesterday and got to the last step (test the RCBO) and on 3 attempts the main RCD went instead. TT installation, no markings on front of RCD but assume must be 30mA non time delay.
The obvious answer is quote them to swap for a type S RCD but it's a big 3 phase one and will be expensive!
My main problem is what to do about certificating? I've commisioned the circuit as everything else tested fine and even if the RCBO I've put in was faulty it still met disconnection times because of the main RCD tripping.
It's a 6A lighting circuit. Strangely enough there are loads of other RCBOs on the board too so I can only assume that these either haven't been tested or someone bypassed the main RCD to do them!
The obvious answer is quote them to swap for a type S RCD but it's a big 3 phase one and will be expensive!
My main problem is what to do about certificating? I've commisioned the circuit as everything else tested fine and even if the RCBO I've put in was faulty it still met disconnection times because of the main RCD tripping.
It's a 6A lighting circuit. Strangely enough there are loads of other RCBOs on the board too so I can only assume that these either haven't been tested or someone bypassed the main RCD to do them!