Effectively the cable is run above a very thin layer of the ceiling i.e. the plaster covering the cable.
The cable itself is not protected against penetrative impacts such as nails and screws.
There is no indication that the cable is present as it has been plastered over.
A significant possibility exists that the ceiling may need to be repaired or an item may need to be fixed to a ceiling within the lifetime of the installation.
In the case of someone working on or at the ceiling, since it is not possible to identify that the cable is there, someone may damage the cable inadvertently, giving rise to the possibility of electric shock.
This is something that is to be avoided in the installation of a cable and there are no options specified to prevent this for your cable type and installation location.
Whilst approved document P can be a little woolly in its wording it does state that electrical installations should be designed to comply with BS7671.
The cable itself is not protected against penetrative impacts such as nails and screws.
There is no indication that the cable is present as it has been plastered over.
A significant possibility exists that the ceiling may need to be repaired or an item may need to be fixed to a ceiling within the lifetime of the installation.
In the case of someone working on or at the ceiling, since it is not possible to identify that the cable is there, someone may damage the cable inadvertently, giving rise to the possibility of electric shock.
This is something that is to be avoided in the installation of a cable and there are no options specified to prevent this for your cable type and installation location.
Whilst approved document P can be a little woolly in its wording it does state that electrical installations should be designed to comply with BS7671.