DT1991
From BS5839
The circuits of fire alarm systems need to be segregated from the cables of other circuits to minimize any potential for other circuits to cause malfunction of the fire alarm system arising from:
— breakdown of cable insulation of other circuits and/or fire alarm circuits;
— a fire caused by a fault on another circuit;
— electromagnetic interference to any fire alarm circuit as a result of the proximity of another circuit;
— damage resulting from the need for other circuits to be installed in, or removed from, ducts or trunking containing a fire alarm circuit.
In order to facilitate identification of fire alarm circuits, cables should preferably be red in colour, unless another form of colour coding is appropriate. By this means, the possible need for appropriatesegregation can be identified, and there will be less likelihood of inadvertent manual interference with the circuits of fire alarm systems (e.g. during work on other electrical circuits).
Basically fire cables should not be next to any other cable/system.
This is not a fire alarm system cable.