Client refusing spd | on ElectriciansForums

Discuss Client refusing spd in the UK Electrical Forum area at ElectriciansForums.net

Joined
May 3, 2018
Messages
32
Reaction score
6
Location
Leicester
Got a customer refusing to pay additional for an spd, its in luton which i believe is known for lightning strikes .
Customer just wants me to install new standard bg board.
Normally, i wouldn't make a fuss, but because its in a lightning zone, im thinking if its mandatory. Or could i put it down as a departure.
 
Did you do the RA as per regs? If so then you cannot force SPD on a customer, just note the refusal on the EIC.
I didn't do the calculations, so technically no. But I know he lives near a substation, he's in the density zone as demonstrated in bs7671, plus he lives near the airport where a lightning strike recently happened. My judgment tells me i should but can't really enforce it. Its a pme system.
In all fairness even if I did a risk assessment hel Probably refuse.
Just gonna put it down as a departure and refusal.
 
As an aside, how does anyone actually do the equation from 7671 when there are factors in it that it's unlikely you'll be able to know accurately? I can't see the point of it might as well have made fitting them mandatory and the cost is just part of the overall cost of the cu a far as the customer is concerned
 
As an aside, how does anyone actually do the equation from 7671 when there are factors in it that it's unlikely you'll be able to know accurately? I can't see the point of it might as well have made fitting them mandatory and the cost is just part of the overall cost of the cu a far as the customer is concerned
Yeah its not really clear whether its mandatory or not.
 
Remember BS 7671 is NOT a mandatory document.
I know, but you've got to have a good reason to depart from it. My point in this case (& I am away without my book) is that the method that it gives in order to assess whether or not an sdp is required, needs information which I don't know how you would obtain, ( in most cases) therefore rendering the equation pointless, therefore why bother with it, just include fitting spd s as a standard requirement.
Although I personally can't see the point of them in the majority of cases, I don't think I know of anyone who has suffered damaged property as a result of overvoltage. But as the price and availability of SPD s has improved, why worry, just fit them.
 
I know, but you've got to have a good reason to depart from it. My point in this case (& I am away without my book) is that the method that it gives in order to assess whether or not an sdp is required, needs information which I don't know how you would obtain, ( in most cases) therefore rendering the equation pointless, therefore why bother with it, just include fitting spd s as a standard requirement.
Although I personally can't see the point of them in the majority of cases, I don't think I know of anyone who has suffered damaged property as a result of overvoltage. But as the price and availability of SPD s has improved, why worry, just fit them.
It depends on what type of spd, if a house has a lot of electronics, leds etc then type 2 spd may offer that protection from sharp overvoltages.
I tend to just do a quick research on the area, like nearest substation, type of supply, and whether its prone to lightning strikes. Based on that i make a quick judgement, haven't got time to faff around with the equations, more suitable for a dedicated designer.
 
Is this a residential property?

If it is, there is absolutely no requirement to do an assessment, or install spd in lieu of an assessment.

For a single property it is only where the cost of impact outweighs the cost of the protection would such protection be necessary.

If the customer believes the potential impact does not justify the cost of spd he is 100% correct.

It isn't an exception to the regs, it is completely in compliance with the regs.
 
Is this a residential property?

If it is, there is absolutely no requirement to do an assessment, or install spd in lieu of an assessment.

For a single property it is only where the cost of impact outweighs the cost of the protection would such protection be necessary.

If the customer believes the potential impact does not justify the cost of spd he is 100% correct.

It isn't an exception to the regs, it is completely in compliance with the regs.


Surely the cost of the protection is only about ÂŁ70 or under now, a lightning strike can destroy the consumer unit for a start let alone TV, smart phone, computer etc etc. How can you say the cost of protection outweighs the cost of impact?

The way I get round it when a customer asks what an SPD is and do I need it I give them two options...

1. You can pay the ÂŁ70 for the SPD which experts have decided is worth the protection and you can have some piece of mind that you have at least some protection from lightening strikes.

2. I can do a very complicated risk assessment that will often still dictate you need the SPD, to carry out this risk assessment I charge ÂŁ90.

Would you like choice 1 or choice 2?

Any customer who would moan that much about fitting an SPD frankly I dont want as a customer, go find some cowboy to do your electrics.
 
Surely the cost of the protection is only about ÂŁ70 or under now, a lightning strike can destroy the consumer unit for a start let alone TV, smart phone, computer etc etc. How can you say the cost of protection outweighs the cost of impact?

The way I get round it when a customer asks what an SPD is and do I need it I give them two options...

1. You can pay the ÂŁ70 for the SPD which experts have decided is worth the protection and you can have some piece of mind that you have at least some protection from lightening strikes.

2. I can do a very complicated risk assessment that will often still dictate you need the SPD, to carry out this risk assessment I charge ÂŁ90.

Would you like choice 1 or choice 2?

Any customer who would moan that much about fitting an SPD frankly I dont want as a customer, go find some cowboy to do your electrics.
I am not making any judgement on the validity of the decision, I am merely pointing out what is specified by the regulations.

The idea that no spd is wrong, is not what is stated in the regulations, the regulations are clear in this area.

I also find it somewhat disingenuous to suggest that someone following the regulations would therefore be a cowboy!
 

Reply to Client refusing spd in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
433
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This potential client seems to be making progress in terms of being interested in proper chargers and answering my query questions. I have also...
Replies
13
Views
2K
Problems can arise when you get on too well then they think he won’t mind me doing a bit.
    • Friendly
    • Like
Replies
8
Views
483

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top