tom262

PHP:
Hello, yesterday I Carried out a EICR, two DBs all installed in 2007, so pretty simple until I got to the last circuit. And It was a 16amp type B marked up as bathroom socket, thinking it was most likely the shaver points, after half hour I found a weatherproof socket under the bathroom sink, attempted to take a Zs from it and found there was no earth, after another half hour of ****ing around I found a 230v to 230v transformer?! Which fed the socket,

if someone could tell me how to upload photos, I will show you.

is this ok?! Apparently it was installed by a previous owner, I've disconnected it as they don't use it anyway but seems abit strange.
 
Because it 'electrical separation' there's no earth return path, but how would you know weather this satisfies the disconnection times, I know it dose on the supply side of the transformer but what about the secondary side..?? I've taken all my readings, zs, rcd ect from the supply side but as there's no earth by tester 'fluke' won't take it from the secondary side.

Ok, as Andy78 has rightly said, forget disconnection times for now. However, this question reveals a fundamental lack of understanding of what actually constitutes a protective measure, yet you're carrying out PIRs? Take note of the two phrases I have highlighted in bold for you and have a think as to why they should not be in the same sentence.


No it's not normally, but it's a lot more helpful than some people on here!!
its in zone 3.

Where's zone 3?
 
Ok, as Andy78 has rightly said, forget disconnection times for now. However, this question reveals a fundamental lack of understanding of what actually constitutes a protective measure, yet you're carrying out PIRs? Take note of the two phrases I have highlighted in bold for you and have a think as to why they should not be in the same sentence.




Where's zone 3?

Parazone.......the bottle of bleach under the sink.......?
 
Ok, as Andy78 has rightly said, forget disconnection times for now. However, this question reveals a fundamental lack of understanding of what actually constitutes a protective measure, yet you're carrying out PIRs? Take note of the two phrases I have highlighted in bold for you and have a think as to why they should not be in the same sentence.




Where's zone 3?
seems he is being naughty and testing installs to old regs.

apart from no earth there is no problem with an outdoor socket but there is a problem with the type of appliances and things e.g. hair driyers etc that will get used in there.


in my opinion i would note it should be removed, (you cant just disconnect things without the clients permission)
 
seems he is being naughty and testing installs to old regs.

apart from no earth there is no problem with an outdoor socket but there is a problem with the type of appliances and things e.g. hair driyers etc that will get used in there.


in my opinion i would note it should be removed, (you cant just disconnect things without the clients permission)

Apart from no earth??? Read the OP again, it's supplied by an isolating transformer and so is using electrical separation as it's method of protection.

What danger do you forsee in using such appliances?
 
Apart from no earth??? Read the OP again, it's supplied by an isolating transformer and so is using electrical separation as it's method of protection.

What danger do you forsee in using such appliances?
the regs allow shaver sockets etc at 110v and 240v not appliances.

it would be a depature from the regs and would need a risk assement carrying out or could land you in hot water in the future if anyone gets a shock
 
Last edited:

Reply to Confused....bathroom socket in the UK Electrical Forum area at ElectriciansForums.net

Recommended Sponsor News

Exclusive Forum Offer! Free euro 2024 wall chart for first 10 responses!

Hi everyone,

We have 10 exclusive Uheat EURO 2024 Wallcharts to giveaway for Electricians Forum Members! The first 10 people to reply YES to this thread - I will message and get them sent out to you just in time for this years tournament! GO GO GO

Quickwire Now Sponsor ElectriciansForums.net

I am sure you will join me in welcoming our newest sponsors of ElectriciansForums.net - Quickwire! They have decided to join us after seeing you guys discussing their products here. Now we have an expert on board that you can chat to @Quickwire-Sam who will be happy to answer your queries!

[ElectriciansForums.net] Quickwire Now Sponsor ElectriciansForums.net


@Quickwire-Sam said "At Quickwire, we're all about speed, safety, and reliability. We're a family-run business, and every Quickwire connector is proudly made right here in the UK, ensuring noticeable quality. In short, Quickwire is the fastest connection method on the market. Whether you're an experienced electrician or a DIY enthusiast, Quickwire makes electrical connections ridiculously quick and easy. We're passionate about blending British craftsmanship with innovation. If you have any questions or if there's any way we can help, please just ask me!"

PCBWay Now Sponsor ElectriciansForums.net!!

I hope you will all join me in welcoming our newest sponsor to the forum PCBWay! You can contact their friendly people by sending a message to @PCBWay who will be happy to answer your queries.

Welcome to the community and thanks for your sponsorship!

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

PCBWay provides services including PCB Prototype and batch Production, PCB Assembly (SMT), 3D Printing, CNC Machining, PCB Design, Electronics Modules Selling, etc. We are committed to meeting the needs of global makers from different industries in terms of quality, delivery, cost-effectiveness, and any other demanding requests in electronics.

[ElectriciansForums.net] PCBWay Now Sponsor ElectriciansForums.net!!

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top