Running a 20A 6.0mm T&E radial to utility room to supply two single 13A sockets to feed Washing Machine and Tumble Dryer.

The T&E will be terminated in a PVC adaptable box, just wondering how to make the connection to the sockets as terminals
will not take 6.0mm.

Can I use connector strip using 4.0mm or 2.5mm to feed the sockets, was hoping to use Wago but they too will not take 6.0mm.
Is there connector out there that will do the job.

Thanks
 
As you already have 6mm installed use that (as you said) then use 2.5mm for the additional sockets
20A MCB is fine for protection

One advantage is you will have a very good Zs reading

I think 6.0mm and 2.5mm in the same terminal is more likely to result in an unsound connection than two (6mm or otherwise) conductors of the same CSA,as there is a risk that the smaller CSA wire will not be clamped once the screw is on the 6mm.
Just to clarify I dont believe a 6.0mm radial for the scenario the OP has described is ever a good idea...the point I was making is that despite what others have said it IS possible to satisfactorily terminate two 6mm conductors in a quality socket with a 35mm minimum back box.If you cant do it dont blame the gear.
 
I've stated it's ''possible'' but i wouldn't like to to rely on those terminations for the reasons given previously. Not that i would even think about having twin 6mm cables supplying 13A socket outlets of any description...

As for using differing cable CSA, it doesn't quite work that way. The screw will have enough space to deform both the 6mm and the 2.5mm. In the case of 2 X 6mm, there is no space to deform conductors the terminal space as it's at it's maximum capacity!!

Who's blaming the gear?? It's those that contemplate stringing socket outlets together with 6mm cable thats Bonker's...
 

Reply to Connecting 6.0mm T&E in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
One thing you may find is that it will most probably be a 6mm cable and to get two of them in to a terminal may prove to be a stumbling block if...
Replies
3
Views
1K
  • Question
CONCLUSION (Couldn't see how to edit title) It was not belting it down with rain today, so lifted the manhole cover. The pump is about 2 metres...
2 3 4
Replies
45
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top