A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
2392-10 : Division of Installation .
If we look atRegulation 314.1. :coolgleamA:
The Choice is Your as Designer(s) .
314.1 . does not mention . Thata Ring Final Circuit should be the Automatic Choice for Socket – outlets
Ring Final Circuit .
Radials
Apprentices
Important to remember that where a Residual Current Device does not ( Incorporate OvercurrentProtection ) A Circuit Breakermust be Used . :gettree:
Something I knocked up . ( PIR ) one day ??
Regulations . 612.2.1. ( R2 ) Continuity of ProtectiveConductor(s) . :banghead:
Apprentices .
There’s to much writtenabout Ring Final Circuits . Method 1
Method 2 (- usesthe Wander Lead or ( R2 ) Method
Mainly used on MainProtective Bonding Conductor .
Reason : You must Confirm the Continuity of Main Protective Bonding Conductor . ( A ◄► B )
Firstly : Permission beforehand as this may have SafetyImplications . “ IMPORTANT
i) Safe Isolation . before you begin .
ii) Disconnect any Parallel Paths . This can be done byDisconnecting ◄► MainProtective Bonding Conductor . from the ( MET)
iii) Disconnecting ◄► MainProtective Bonding Conductor . from BS-951/ Earth Clamp .
-&-s . Null the leads . Why ?? . Wander Lead will add aconsiderable résistance to your Instrument .
-&-s . Instrument does NOT have a Null function . Subtract the résistancefrom the Actual Reading .
-&-s . Readingcan be recorded as the Résistance of the ( CPC / R2 ) on the Schedule of Test Results . Example .Regulation . p/341 . Continuity ( R2 * / ) Dead Test
Remember (- -&-s . to Reconnect Parallel Paths . )
-&-s . Earthing Clamps must conform to BS-951 / “Safety Electrical Connection – Do Not Remove “ Etc
Remember . Anything to do with Earthing . -&-s are allover you like a Bad Rash . Yeah :gettree:
Apprentices : amUsing the Wording to help you Understand someConcepts of Earthing . Regulation .P/32 . fig2.1 :26:
From the ( Service Cut-out ) 16.0mm[SUP]2 [/SUP]Earthing Conductor to the → ( MET ) → 10.0mm[SUP]2 [/SUP]Gas / Water (- MainProtective Bonding Conductor .
Safety EarthConnection . Do Not Remove .
TT System (- EarthingConductor from the ( MET ) → Earth Electrode .
TT System ( MET ) → 10.0mm[SUP]2 [/SUP]Gas / Water (- MainProtective Bonding Conductor .
541.13. Warning Notices : Earthing & BondingConnections
SafetyElectrical Connection . Do Not Remove .
The Magnetic Mechanism usesa solenoid with an Iron piece . Etc .Used for ( Short-Circuit Currents / Fault Protection )
Thermal Mechanism .
This mechanism uses a ( Heat Sensitive Bimetal Element) it is Used for ( Overload Circuit Protection )
Advantages . Immediate indication of ( Fault Current) by Identifying which circuit the ( Fault )occurred on
Advantages . Reclosing can be Effected at Once after the ( Faulthas been Cleared )
Apprentices : Learning Curve . Point to Note :
RCDs . Because the RCD trips in milliseconds ( mS ) 30 / milliamps. ( mA )
Regulation . Definitions – p/29 ( RCCB ) :speechless:
• The Short Circuit doesNOT Produce an Imbalance between the Line & Neutralcurrents in the ( RCCB ) They are still out there on the 16[SUP]th[/SUP]Edition .
• The ( RCCB ) does Not Incorporate an OverloadFunction .
UsefulJunk :
MCB – The difference being it has Three-States in can be . ( OFF) ( ON ) → ( Tripped )
CircuitBreaker : is designed with a ( Switch ) in orderto Turn a Circuit – ON / OFF .
(can be used for Isolation / FunctionalSwitching ) Table 53.2.
Miniature Circuit Breaker . ( MCB) :earmuffs:
AdvantagesCan operated by Hand or Automatically .
• The Automatic Operationis done by Using . Magnetic or Thermalmechanism
Thisis a Sub-Board . ( Main Board is Isolated / LockedOFF ) :speechless:
ThisTest in done on the 16[SUP]TH[/SUP] Edition ( No- RCDs ) … Just Main Switch 100A . Example
Insulation Résistance Test (IR )
Example(- 6 / Way
ThirdTest:
Dead Test /Safe Isolation procedures should be carried out . Priorto Testing
Thiscan be carried out at the Main Switch ( 100A ) at the Distribution Board . being Tested
Youmust Insure that the ( Switch ) in the ( On-position ) with allthe ( Circuit breaker(s) for all circuits to be Tested .
indoing this . ( You must Insure that – all Lamps / Dimmer switches or Appliancesare RemovedPrior toTest
theTest is carried out between the ( Line & Neutral ) Usingan Insulation Résistance Tester / set on( 500V / M. Scale )
500V Scaleis Applied / A reading should be Greater that ( 999 . is Obtained )
TheTest is then carried out On .
theTest is carried out between the ( Line & Earth ) Using an InsulationRésistance Tester / set on ( 500V / M . Scale )
theTest is carried out between the ( Neutral &Earth ) Using an InsulationRésistance Tester / set on ( 500V / M . Scale )
Thisproves that the ( Line & Neutral ) arenot Touching .
Thisproves that the ( Neutral & Earth )arenot Touching .
Thisproves that the ( Line & Earth ) are not Touching .
(No Breakdown of the a ConductorInsulation ) -&-s
MCBs/ Red or Green indicator provides Immediate Visual Indication of Devices
ForIsolation Functions (- Green / OFF . Red / ON .
Inspection& Testing , before an Installation is Fully Commissioned is a Critical Task. :53:
Visual &Testing “
:juggle2:
Apprentices & 2392-10 . Ring Final Circuit .
This is just the same as if you where doing it onConsumer Unit ( DEADTEST )
On Industrial Premises’ .
When doing Insulation Resistance Testing on a Ring Final Circuit it have to “ BeIndividually . ( IR ) as it is NOT Possible to carry out InsulationResistance on Industrial Installation as a Hole ’ . Yeah
Firstly . Ring Final Continuity Checks .
This is done by disconnection of Both Ends of the Line ( Neutral &Circuit Protective Conductor ) from the Board.
Continuitycan be Checked for Each Conductor .
Check : Null out yourLeads / Megger 1552 .
Step - 1. Line to Line . 0.26Ω . ( Lower )
Step - 2 . Neutralto Neutral . 0.26Ω . ( Lower )
Step – 3 . CPC to CPC . is aReduced Cross-Sectional Area its Résistance . ( Which then is “ Higher than the Phases0.33Ω .) being/ Line / Neutral
Next Step .
( DB ) “ Distribution Board “Cross/ Connect . Neutral to Line. Vice. Versa
( DB ) “ Distribution Board “Cross/ Connect . Line toNeutral
The Résistance of the ( Line& Neutral Résistance at any SocketOutlet ) Readingshould be the Same . ? 0.15Ω
IndustrialInstallation / Wired in Single(s) Core CablesSame Size “ ???
If Readings ( Increase ) from point of supply . You may have ( Mixed ) up the Line& Neutral Conductors . off the Two Legs of the Ring .
Double Check (- The Readings should be ??
Line :0.26Ω
Neutral: 0.26Ω + ( 0.26Ω + 0.26Ω = Combined 0.52Ω )
¼ Combined : 0.13Ω
Spurs “ will give a SlightlyHigher Reading(s) it will give the Résistance of the Spur Conductors’ .
Next Step . ( Final )
( DB ) “ Distribution Board “Cross/ Connect . Lineto CPC . Vice. Versa … Readings / ( R1 + R2 )
( DB ) “ Distribution Board “Cross/ Connect . CPCto Line .
The Résistance of the ( Line& CPC Résistance at any Socket Outlet ) Readings / ( R1 + R2 ) Polarity checked at this Stage . as well as Visual Inspection on Terminals .
The reading should be the Same ( ¼ Combined Résistance : ofthat of the Line &CPC .
Spurunits will be Slightly Higher .
The Highest Reading Obtained . will be Recorded . ( R1 + R2 ) Schedule of TestResults. ( Line / 0.22Ω + Neutral / 0.23Ω) R2CPC /0.3 . ( R1 + R2 ) 0.52Ω
Whilst the Ring Conductors are Disconnected it make sensethe do Insulation Résistance Test . at this Point .
2392-10 / Some Regulation for Installing a ConsumerUnit : The WHY.S :speechless:
416.2. - Note : Barriers or Enclosures are Intended to prevent ( Contact with Live Parts )
(- Cable Entry Sealed to ( IP4X ) 416.2.2.Horizontal Top Surface of a Barriers or Enclosures .
(- Enclosures Sealed to ( IP2X i.e. BLANKS FITTED )
ii) After disconnection of the Supply to ( Live Parts ) againstwhich the Barriers or Enclosures afford ( Protection ) Restoration of theSupply being possible ( ONLY ) after
replacement orReclosure of the ( BARRIER or ENCLOSURES ) Etc .
(- Sufficient Space to allow Cables to Bend into Devices .
MechanicalStresses . 522.8.3.
The ( Radius ) of every ( Bend ) in a wiring systemshall be such that conductors or Cables do not suffer ( Damage & Terminals are NOT Stressed )
Plain English(- Such that Conductors’ & Cables shall NOTsuffer Damage )
:13:
This is Whatyour Assessor is Looking for . - (- Cables Sheaths NOT stripped Outside ofEnclosures . 526.9.
Cores of ( Sheathed Cables ) from whichthe Sheath has been Removed & Non-sheathed cables at the termination ofConduit . Ducting or Trunking shall be Enclosed as required by Regulation .526.5.
(- EnclosureMaterialAppropriate to the Environment . 522.6.1.
Wiring Systemsshall be selected & Erected so as to Minimize Mechanical Damage . e.g. .damage due to Impact . Abrasion . Penetration . Compression or Tension . DuringInstallation .
( T ) (- Diagrams “ must be Provided .514.9. / 514.12.1.
A legibleDiagram . Chart or Table or equivalent form of information shall be providedindicating in particular . ( Circuit Detail Labels )
(- Unit Adequately Fixed . 416.2.3.
A Barrier orEnclosure shall be Firmly Secured in Place . ETC
Division ofInstallation . 314.1.
InstallationCircuit Arrangement . 314.4.
Protected byAppropriate Devices . MCBs – 433.1.1. / Protection by One Device ( iii )
514.8.1.Identification of a Protective Device : MCB .
A ProtectiveDevice shall be arranged & Indentified so that the Circuit Protected may beeasily Recognised .
511.1 ) Complieswith the relevant requirement of the applicable British Standard / Harmonised Standard .
510.2. ) ManufacturesInstructions are followed .
TheProtective Devices in the Consumer Unit are adequate for the Prospective FaultLevel . Conditional rating . ??
313.1/ 512.1.2. ( ii )
TheRating of the MainSwitch or Circuit Breaker is sufficient for the Likely Electrical Load .512.1.2. ( i )
The( Tails ) between the Consumer Unit & the (Meter ) or DNO / Isolating Switch . ( Note– An Isolator is often Not Installed bythe Distributor ) O.S.G. p/15
Adequately( Sized ) & Protected against Mechanical Damage .
523.1. )
522.6.1) AG
522.8.1.) AJ .
433.1.1.)
Wire Résistance :
What affects the Résistance of a Wire . :15:
Answer : ConductiveElectrons moving through thewire bang into Electrons attached to Atoms . “ Facts “ This converts some ofthe Electrical Energy to Heat .
The effects the Résistance in Wires :
Length :
Cross-sectional area :
Material : ! Copper .
Temperature : °C
***Cont../ Useful Information for Electricians & Apprentices***