O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
Certification& Reporting :

631.2.

Upon completion of theperiodic inspection & testing of an existing installation . an ElectricalInstallation Condition Report . based on the model given in Appendix 6 . shallbe provided . Such documentation shall include details of the extent of theinstallation and limitations of the inspection & testing covered by theReport . together with records of inspection . the results of testing and arecommendation for the interval until the next periodic inspection . :13:



 
631.3.

Where minor electrical installation work does not include theprovision of a new circuit . a Minor Electrical Installation Work Certificate .based on the model given in Appendix 6 . may be provided for each circuitaltered or extended as an alternative to an Electrical Installation Certificate. :13:


 
631.4.

Electrical Installation Certificates . Electrical InstallationCondition Reports and Minor Electrical Installation Work Certificates shall becompiled and signed or otherwise authenticated by a competent person or persons. :13:


 
631.5.

Electrical Installation Certificates . Electrical InstallationCondition Reports and Minor Electrical Installation Works Certificates may beproduced in any durable medium . including written and electronic mediaregardless of the media used for original certificates . reports or theircopies . their authenticity and integrity shall be verified by a reliableprocess or method . The process or method shall also verify that any copy is atrue copy of the original . :13:


 
560.9. Emergency Lighting Systems .

Emergency Lighting Systems . shall comply with the relevant partof BS-5266 series .

560.10. Fire Detection and Fire Alarm Systems .

Fire Detection and Fire Alarm Systems . shall comply with the relevantpart of BS-5839 series . :13:


 
Table41.1. .

411.3.2.2.
Themaximum disconnection time stated in Table 41.1 shall be applied to finalcircuits NOT exceeding 32A . :crazy:

Maximum disconnection times . ( No change on number ) 0.4 / 0.2 . Etc .

Bottom . Table 41.1.

Where . in a TT system . disconnection is achieved by anovercurrent protective device and protective equipotential bonding is connectedto all the extraneous-conductive –parts within the installation in accordancewith Regulation 411.3.1.2. the maximum disconnection times applicable toa TN system may be used .

Uo is the nominal a.c. r/ms or d.c. Line voltage to Earth .

Where compliance with this regulation is provided by an RCD . thedisconnection times in accordance with . Table 41.1 relate to prospectiveresidual fault currents significantly higher that the rated residual operatingcurrent of the RCD .

Note : Disconnection is not required for protection againstelectric shock but may be required for other reasons such as protection againstthermal effects .


 
416.2.4.

Whereit is necessary to remove a barrier or open an enclosure or remove parts ofenclosures . this shall be possible only .

(i) Still the same – 17[SUP]th[/SUP] Edition.
(ii)Still the same – 17[SUP]th[/SUP] Edition .
(iii)Still the same – 17[SUP]th[/SUP] Edition .

Note: This regulation does not apply to :

A ceilingrose complying with BS-67
* A Cord operated switchcomplying with BS-EN 60669-1 . FirstAmendment :sunny:
A bayonetlampholder complying with BS-EN 61184
AnEdison screw lampholder complying with BS-EN 60238.

* A Cord operated switchcomplying with BS-3676 . – 17[SUP]th[/SUP] Edition.
 
411.4.7. No Change . “ First Amendedment

Wherea circuit breaker is used to satisfy the requirements of regulation 411.3.2.2 or regulation 411.3.2.3. . Themaximum value of earth fault loop impedance ( Zs ) shall be determined by the formulain regulation 411.4.5 . Alternatively . for a nominal voltage ( Uo ) of 230Vand a disconnection time of ( 0.4s ) in accordance with Regulation 411.3.2.2.or ( 5s ) in accordance with Regulation 411.3.2.3. The values specified intable – 41.3. for the types and ratings of overcurrentdevices listed may be used instead ofCalculation .

 

Appendix 1 . ( Normative) :13:

BS-EN 60898:1991 .
Specificationfor circuit-breakers for overcurrent protection for household & similar installations’.
Replacedby BS-EN 60898-1 : 2003 . but remains current .

BS-EN 60898-1 : 2003 . Circuit breakers for A.C. operation .

BS-EN 60898-2 : 2001 . Circuit breakers for A.C. & D.C. operation . BS-EN 60898-2: 2001 . remains current ( it was withdrawn in error and has been reinstated )




 
Electrical Installation Certificate– Guidance for Recipient ( to be appended to the Certificate ) 17th Edition p- 334 / First Amendedment :13:

ThisCertificate is intended to be issued only for a new electrical installation orfor new work associated with an addition or alteration to an existinginstallation . it should not have been issued for the inspection of an existing electrical installation . An “ ElectricalInstallation Condition Report “should be issued for such an inspection .


 
First Amendedment : Just a Reminder . :13:

Electrical Installation Condition Report “ p-396

Domestic□Commercial □ Industrial □ other ( include brief description )

Extent& Limitations of Inspection & Testing .
Extentof the electrical installation covered by this report . …………………..

Agreedwith : ……..
Operationallimitations including the reasons ( Regulation 634.2. )

( Regulation 634.2. )
Anydamage . deterioration . defects . dangerous conditions and non-compliance withthe requirements of the Regulations . which may give rise to danger . together withany significant limitations of the inspection & testing . including theirreasons . shall be recorded .

Summaryof the Condition of the Installation .
Generalcondition of the installation ( in terms of electrical safety )

… Overall assessment of the installation interms of its suitability for continued use .
SATISFACTOTY/ UNSATISFACTOTY ( delete as appropriate )
*An unsatisfactory assessment indicates that dangerous ( Code C1 ) and / orpotentially dangerous ( Code C2 ) conditions have been identified

Recommendations:
Wherethe overall assessment of the suitability of the installation for continued useabove is stated as UNSATISFACTOTY . I / we recommend that any observationsclassified as “ Danger present “ ( Code C1 ) or potentially dangerous ( Code C2 ) are acted upon as a matter ofurgency .
Investigationwithout delay is recommended for observations identified as “ further investigation required
Observationsclassified as “ Improvementrecommended “ ( Code C3 ) should be given due consideration .

Oneof the following codes . as appropriate . has been allocated to each of theobservations made above to indicate to the person(s) responsible for theinstallation the degree of urgency for remedial action .

C1 – Danger present . Risk of injury . Immediate remedial actionrequired .
C2 – Potentially dangerous – urgent remedial action required .
C3 – Improvement recommended .



 
17[SUP]th[/SUP]Edition / FirstAmendedment . :13:

612.2.1. No change .
612.2.2. No change .
612.3. No change .
612.3.1. No change .
612.3.2. No change .
612.3.3. No change .
612.4. No change .
612.4.1. No change .
612.4.2. No change .
612.4.3. No change .
612.4.4. No change .
612.4.5. No change .
612.5. No change .
612.5.1.
612.5.2. Any insulation or insulating arrangement of extraneous -conductive-partsintended to satisfy Regulation 418.1.4. (iii)
(i) when tested at 500V d.c.shall be not less than I megohm . &
(ii) shall be able to withstand a test voltage of at least 2kV a.c. r/ms . &
(iii) shall not pass a leakage current exceeding 1mA in normal conditions of use .

612.6. No change .

612.7. Where the earthingsystem incorporates an earth electrode as part of the installation . theelectrode résistance to Earth shall be measured .
Note : Where a measurement of ( Ra ) is not practicable themeasured value of external earth fault loop impedance may be used .

612.8.No change .
612.8.1.
a) TN- No change .
b) TT- No change .
c) IT- Compliance withRegulation 411.6. shall be verified by calculation or measurement of thecurrent ( Id ) in case of a first fault at the line conductor or at the Neutral.

Note 1 : The measurement is made only if calculation is notpossible because all the parameters are not known . Precautions are to be takenwhile making the measurement in order to avoid the danger due to a double fault.

Where conditions that are similar to conditions of a TT systemoccur . in the event of a second fault in another circuit ( see Regulation411.6.4. (ii)) verification is made as for a TT system ( see point b ) of this regulation .

Where conditions that are similar to conditions of a TN systemoccur . in the event of a second fault in another circuit ( see Regulation411.6.4. (i)) verification is made as for a TN system ( see point a ) of this regulation .

Note 2 : During measurement of the fault loop impedance . it isnecessary to establish a connection of negligible impedance between the neutralpoint of the system and the protective conductor preferably at the origin ofthe installation or . where this is not acceptable . at the point ofmeasurement .

612.9.No change .
612.10.No change .
612.11.No change .
612.12.No change .
612.13.1.No change .
612.14.No change .

 
860.8. – Wiring Systems . :leaving:

560.8.1. One or more of thefollowing wiring systems shall be utilised for safety services required tooperate in fire conditions .

i) Mineral insulated cable systems complying with BS-EN 60702-1 and BS-EN 60702-2 and BS-EN60332-1-2.
ii) Fire-resistant cables complying with IEC 60331-1 or IEC60331-2 or IEC 60331-3 and with BS-EN 60332-`1-2.
iii) Fire-resistant cables complying with test requirements of BS-EN 50200or BS-8434 or BS-8491 . appropriate for the cable size and with BS-EN60332-1-2.
iv) A wiring system maintaining the necessary fire and mechanicalprotection .

the wiring system selected shall meet the requirements of the relevantcode of practice appropriate to the application and shall be mounted andinstalled in such a way that the circuit integrity will not be impaired during afire .

Note 1 : The codes of practice in the UK for emergency lighting . firealarms and life safety and fire fighting applications are :
i) BS 5266 Part 1 : Fire detection and fire alarm systems forbuildings – Code of practice for system design . installation . commissioningand maintenance .
ii) BS 8519 : Code of practice for the selection and installationof fire-resistant cables and systems for life safety and fire fightingapplications .

Note 2 : BS 5266 . BS 5839 & BS 8519 specifies cables to BS-EN 60702-1. BS 7629-1 & BS 7846 as being suitable when appropriately selected for theapplication .

Note 3 : Examples of a system maintaining the necessary fire andmechanical protection could be :
i) Constructional enclosures to maintain fire and mechanicalprotection . or
ii) Wiring systems in separate fire compartments .

560.8.2. Wiring for control and bus systems of safety servicesshall be in accordance with the same requirements as the wiring which is to beused for the safety services . This does not apply to circuits that do notadversely affect the operation of the safety equipment .

560.8.3. Deleted by BS-7671:2008 . Amendment No 1 & reserved for future use .

560.8.4. Circuits for safety services which can be supplied bydirect current shall be provided with ( Two-pole ) Overcurrent protection mechanisms .

560.8.5. Switchgear & controlgear used for both a.c. & d.c. supply sources shall be suitable for both a.c. &d.c.operation .

650.8.3. Deleted byBS-7671:2008.

The wiring between the safety source and the main distribution boardshall be erected in such a manner as to reduce to a minimum the risk ofShort-circuit or Earth fault or the risk of fire or danger to persons .





 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
421
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
921
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
881

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top