O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer

FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “

For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag

CookerDesign Current Calculations

Thefirst thing you have to do is get Your Head around the Calculations !!

(From a Design point of View ) 2392-10

DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000

(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps


2392-10/ Domestic Installation Oven(s)

Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )

-Controlled via a CookerSwitch with a Socket outlet .

Asa Designer . we’ll have to Apply Diversity ??

Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .

TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)

DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .

Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.

Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’

-So your Work out the Total Power Rating & then calculate the Full Load Current

Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW

I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A

UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )

I= 33.48 x 30 ÷ 100 = 10.04A

Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .

Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
 
“ Certification& Reporting “ :presents3:

Listfour characteristics of the Electrical Supply that should be recorded on theDocument - this could come Up on-&-s .

313 – Supplies .

313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .

i) The nominal voltage(s) & its characteristics includingharmonic distortion .
ii) The nature of the current & frequency .
iii) The prospective short-circuit current at the Origin of the installation. ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze )
v) The suitability for the requirements of the installation .including the Maximum Demand .
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄

These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄

NOTE : The above information should be provided by distributors’on request ( see Appendix 2 sec 2 )

Appendix 2 – Informative ) Some things have been Changed . inWording .

Definitions- p/39 . ( Ze )
That part of the Earth Fault Loop Impedance which is External tothe Installation ( Ω ) 313.1.


 
Fundamental requirement to understandthe basic principles . Measured / Calculated results and what affect they haveon a circuit . :rofl:

Conductor Résistance .

Whywe divided the Length ( x . mΩ/m figuresby ( 1000 )

Wedivided the length ( x . mΩ/m figures by ( 1000 ) to obtain a résistance value in Ohms .

O.S.G.– 9A )- milli-ohms per meter values . Weneed to covert them to Ohms for our Calculations’ ( dividing by 1000 does this )



 
Chapter 61 :

Initial Verification – Inspection 611 & Testing 612

Initial Verification [ Inspection & Testing ] Therefore helpsto ensure that Electrical Installations are Safe before being put into Service.

611 )- Inspection .

611.1. – Inspectionshall precede Testing & shall normally edone with that part of the installation under Inspection disconnected from theSupply . ◄◄


 
Therequirements of BS-7671:

BS-7671requires that every installation shall be Inspected& Tested to verify that the Regulation(s) havebeen met before [ Being put into Service ]

On completion of an installation or an addition or alteration toan installation . appropriate Inspection & Testing shall be carried out toverify so far as is reasonably practicable that the requirements of thisstandard have been Met .

133.2.1. Voltage :
Electrical equipment shall be suitable with respect to the maximumsteady-state voltage ( r/ms value for a.c. ) likely to be applied . as well as overvoltage’slikely to occur .

Note : for certain equipment . it may also be necessary to takeaccount of the lowest voltage likely to occur .

610.1. Every installation shall . during erection & oncompletion before being put into service . be inspected 7 tested to verify . sofar as is reasonably practicable . that the requirements of the regulation(s)have been Met .

Precautions’ shall be taken to avoid danger to persons &livestock . & to avoid damage to property & installed equipment . duringInspection & Testing .

612 )- Testing . InitialVerification .
612.1. General .
The tests of regulation 612.2. to 13 . Where relevant . shall becarried out the results compared with relevant criteria .

The Test of Regulation(s) 612.2.1. to 612.6. where relevant shall be carried out in thatorder before the installation is Energised .

If any Test indicate a failure to comply . That Test & any precedingTest . the results of which may have been influenced by the fault indicated .shall be repeated after the fault has been rectified

Three Important Tests .

612.2. – Continuity of Conductors .
612.2.1. - Continuity of Protective Conductors including main& supplementary equipotential bonding .

A continuity test shall bemade . it is recommended that the test be carried out with a supply having a (No-load ) voltage between 4V & 24V .ETC.

612.2.2. Continuity of the Ring Final Circuit Conductors .

Your Earthing is your First Line of Defence . ◄◄ :19:
 
( T ) 134.2. InitialVerification . -&-s :19:

134.2.1. During erection& on completion of an installation or an addition or alteration to aninstallation .
& before it is put into service . appropriate inspection &Testing shall be carried out bycompetent persons to verify that the requirements of this Standard have be Met.


 
(T) 711.6. Inspection& Testing .

All TemporaryElectrical Installation(s) ofExhibitions .
Shows& Stands are required to be Inspection& Tested in line with Chapter 61 after EACHASSEMBLY on SITE.

First Amendedment . No change . 711.6.
 
What is the Maximum value of Insulation résistanceof a 230V lighting circuit .

( 1MΩ ) - 612.3.2. – Table 61. 500V / d.c. . -&-s . 2392-10 :19:

612.3.2.
The insulation résistance measured with the test voltage(s) indicatedin Table 61 . shall be conceded satisfactory if the main switchboard and eachdistribution circuit tested separately . with all its final circuit(s)connected but with current-using equipment disconnected . has an insulation résistancenot less than appropriate value given in Table 61.

Note 2 . Insulation résistance values are usually much higher thanthose of Table 61.


Whichof the following is Verified by the Polarity Test . -&-s . 2392-10

A) That there is a separation of live partsfrom other circuit(s) & from earth .
B) The Phase sequence of multi-phasecircuits is maintained throughout the installation .
C) Every fuse &single-pole control & protective device is connected to the line conductoronly . 612.6. & 612.1. :19:
D) All assemblies are properly mounted .adjusted . & installed correctly as required by the reverent regulation(s) .

 
Taken for old Notes .

Calculationwhen the protective device is an RCD orRCBO . :rofl:

ResidualCurrent Devices ( RCDs )

Wherethe installation is part of a TN-system . the basic requirement is given in Regulation 411.4.5. i.e..

Zs x Ia ≤ Uo volts.

Foran RCD ( Ia ) is the rated residual operatingcurrent providing disconnection in the required time .

ForTT systems the additional requirement that ( Ra x I∆n ≤ 50V )is given in regulation 411.5.3. In this requirement ( Ra ) is the sum of the earth electrode résistanceof the protective conductor connecting it to the Exposed Conductive Parts .

Inthe above expression . of course . ( I∆n ) is in amperes . limitingconsideration to residual current circuit breakers ( RCBOs ) to BS-EN 61008 . the values of ( Zs ) & ( I∆n ) encountered in practice are such that there is no difficulty in meeting therequirement given above .

Theearth fault current is limited by the value of ( Zs ) & will be of the same order as occurs when fault protection . is provided byOvercurrent protective devices . It should be checked that the RCD complieswith Regulation 531.2.8. which requiresthat it is capable of withstanding without damage the Thermal & Mechanical Stresses caused by the earth faultcurrent .

Ifan ( RCCB ) to BS-EN 61008 does notincorporate an intentional time delay it is required by the British Standard tooperate within ( 0.04 sec ) at aresidual current of ( 5 I∆n A ) &the designer merely has to check that the circuit is Thermally protected forthat time .

531.2.8.

Wherean RCD is used for fault protection with . but separately from . an Overcurrentprotective device . it shall be verified that the residual current operateddevice is capable of withstanding . without damage . the Thermal &Mechanical Stresses to which it is likely to be subjected in the case of afault occurring on the load side of the point at which it is installed .
 
BS-7671:2008. does not Demand that diversity be taken into account but . for the economicdesign of an installation . diversity cannot be ignored .
Thediversity factors used must be optimistic . an adequate margin of safety mustalways be allowed .

Asindicated in Regulation 433.1. whichgives the general requirement concerning Overload protection .
Circuitsshall be so designed that small Overloads of long duration are unlikely toOccur .

 
Inspection: 2392-10

Carryout the Initial Verification ( Inspection . Testing & Certification ) of aninstallation to BS-7671:2008

As -&-s rightly asks the Q/As . State the Human Senses that may need to be employed the Initial Verification of an Installation .

Definitions p/29Inspection : Examination of an Electrical Installationusing all the Senses as Appropriate . BS-7671:2008 . Amendment No 1 :2011

2392-10. Fundamental Initial Verification of ElectricalInstallation(s) - Three areas to this Unit . :19:
Preparationfor Initial Inspection & Testing .

Inspection.
Testing.
 
General Requirement : :19:

Regulation 6101. ( p/156) - ( p/189)

Every installation shall . during erection and/or on completion beforebeing put into service be Inspected & Tested to verify . so far asreasonably practicable . that the requirements of the Regulation have been Met.

As an Inspector 2391-10 :2392-10 : )- The reason(s) for an Inspection & Test of an ElectricalInstallation is to verify that the installation complies with the Regulationswith regards to its ( Design & Construction )

Asan Inspector )- Carrying out the Inspection to for fill these requirements the Regulations . Call forthe following information to be “ MADE AVAILABLE

Results of the assessment of General characteristics required bySection(s) ( 311. 312 . & 313 . )

Youare looking at .

313.1. General The followingcharacteristics of the supply or supplies . from whatever source . & thenormal range of those characteristics where appropriate . shall be determinedby Calculation . Measurement . Enquiry or Inspection .

i) The nominal voltage(s) & its characteristics includingharmonic distortion . ◄
ii) The nature of the current & frequency . ◄
iii) The prospective short-circuit current at the Origin of theinstallation . ◄
iv) The Earth Fault Loop Impedance of that part of the systemexternal to the installation ( Ze ) ◄
v) The suitability for the requirements of the installation .including the Maximum Demand . ◄
vi) The type & rating of the overcurrent protective device(s)acting at the Origin of the installation . ◄

These characteristics shall be ascertained for an External Supply& shall be determined for a private source . These requirements are equallyapplicable to main supplies & to safety services & standby supplies . ◄

Regulations call for the informationto be made available . ( 514.9. )
( Provide all the necessaryinformation as to circuit type . number of points & their positions . cablesizes . protective device types & their ratings . )

InitialInspection :
611.1. ( p/156 ) – ( p/189 )

Inspectionshall precede testing & shall normally be done with that part of the ( Installation Disconnected from the Supply ) ◄◄◄◄◄◄

Just a Reminder !

Regulation(s) states134.1.1. ( p/19 ) – ( p/21 )
Good workmanship by a Competent Person or Persons under theirsupervision & proper materials shall be used . in the erection of the electricalinstallation . Electrical equipment shall be installed in accordance with theinstructions provided by the ( MANUFACTURES of the EQUIPMENT )

Regulation 612.2. ( p/159 ) – ( p/191 )
Calls for the inspector to confirm that equipment has been selectedin accordance with Section 511 . of theWiring Regulations . & the equipments compliance with the relevant Britishor Equivalent Standard .
 
2392-10:

Of what use to us is the Measuring of Earth Fault Loop or ( Zs ) of the circuit .

Ifwe know the value of it we can use “ Ohm(s) Law “ to calculate the Fault Current that will flow. ( if a FaultOccurs )

Formulawe can apply is ( Voltage = Current ) Résistance .

Wecan see that Fault Current & EarthFault Loop Impedance are directly linked . The lower the Earth Fault Loop theHigher the Fault Current & Vice Versa .
Therefore - The lower the Earth Fault Loop / The Higherthe Fault Current . The quicker the Protective Device will operate to cut theCurrent .

Ifwe limit the Maximum Value of the Earth Fault Loop we can be confident that theFault Current will be of a Higher Magnitude to operate the protective device .
Regulation– 411.3.2. :- Automatic Disconnection inCase of a Fault .

 

Reply to ***Cont../ Useful Information for Electricians & Apprentices*** in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
770
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top