A
amberleaf
O.S.G.. The use of other methods’ of determining Maximum Demand is Not Precludedwhere Specified by the Installation Designer
FirstlyI make no Apologies for the Way am Writing on any Matters . it can be a first day Apprentice or some one Needing aJog of Memory .
Sowe are all in the Same Boat . “ To Learn “
For the Apprentices . The Day we stop learning is the Day we hang Upour Tool-Bag
CookerDesign Current Calculations
Thefirst thing you have to do is get Your Head around the Calculations !!
(From a Design point of View ) 2392-10
DomesticInstallation Oven(s) & Hob(s) are to be Calculated upon their MAXIMUM LOADING
Startwith a simple Calculation ( An Oven has a rating of 2kW ) 2000
(I = P/V ) Formula … I = 2000 ÷ 230V = 8.70A …. Weare Using the Unit Amps
2392-10/ Domestic Installation Oven(s)
Ovenhas 4 Rings ( 2 x 1kW ) & ( 2 x 1.5kW ) & Grill ( 2kW ) & Oven (3kW )
-Controlled via a CookerSwitch with a Socket outlet .
Asa Designer . we’ll have to Apply Diversity ??
Important )- Diversity allowance to be Applied to the FULL LOAD CURRENT for CookingAppliances .
TheO.S.G. is telling us . Purpose of the Final Circuit fed from theConductors )
O.S.G.Table 1B p/97 – column (3) Cooking Appliances → At the Top of the Page Note : Type ofPremises ( 2392-10 → Household Installations ) Domestic Installation(s)
DomesticInstallation(s) Only O.S.G. - 10A + 30% f.l – Full Load ) of connected Cooking Appliances in the Excess of 10A+ 5A if a socket-outlet is incorporated in the Control Unit . ( C.C.U. ) – 45A + 13A Socket Switched with Neon .
Fromyour point of View ( The First 10A ofthe rated current plus 30% of the reminder ( Plus) 5A if the Control Unit incorporates s Socket.
Calculations)- You bank “ Hold OFF“ the first 10 Amps of the Maximum Load Current )
The10A will be used at the End of the Calculations’
-So your Work out the Total Power Rating & then calculate the Full Load Current
Calculations)- Power = ( 2 x 1 ) + ( 2 x 1.5 ) + ( 2+ 3 ) = 10kW
I= 10000 ÷ 230V = 43.48A … round it up to the first four numbers43.47826087 ( 48 ) 43.48A
UsingDiversity allowance stated ↑↑ ( 43.48A sub 10A = 33.48A )
I= 33.48 x 30 ÷ 100 = 10.04A
Youradding the ( 5A ) for Socket outlet . I = 10A + 10.04 + 5A = 25.04A )- Asa Designer this is your Expected Current Demand .
Remember )- Supply Cables Rated to suit DesignCurrent ( Iz ) :)
Definitions– Part 2 . BS-7671:2008 :17:
Bonding Conductor . p/20 .
Aprotective conductor providing equipotentialbonding .
Class1 Equipment . p/21 .
Whereprotection against electric sock does not rely solely on basic insulation alone. Exposed – conductive parts being connected to a protective conductor whiththe fixed wiring of the installation . (See BS-EN 61140 )
Class11 Equipment . p/21 .
Whereprotection against electric shock relies on the application of additional orsupplementary insulation .
Thereis no provision for the connection of a protective conductorto exposed metalwork .
DoubleInsulation . p/23 .
DoubleInsulation ( Class 11 ) Insulation comprising both basic Insulation &supplementary insulation .
Earth. p/23
Theconductive mass of Earth . whose electricpotential at any point is conventionally taken as Zero. ◄◄
EarthElectrode . p/23
Conductivepart . which may be embedded in the soil or in a specific conductive medium .e.g. concrete or coke . in electrical contact with the Earth .
Aconductor or group of conductors in intimate contact with . & providing anelectrical connection to Earth .
EarthElectrode Résistance . p/23 .
Therésistance of an Earth electrode to Earth .
EarthFault Current .
Anovercurrent resulting from a Fault of negligible impedance between a Lineconductor & an Exposed – conductive – part or a protective conductor .
AFault current which flows to Earth .
EarthFault Loop Impedance . p/23
The impedance of the EarthFault current loop starting & ending at the point of Earth Fault . This impedance isdenoted by the symbol ( Zs )
Symbol( Z ) - Unit ( Ω )
TheEarth Fault Loop .
The impedance of the EarthFault current loop starting & ending at the point of Earth Fault . Consists of :-
• The circuit protective conductor ( C.P.C. )
• Consumers Earthing terminal & Earthingconductor
• for TN Systems . Themetallic return path .
• for TT Systems & IT Systems Earth return path .
• The path through the Earthed neutral point ofthe Transformer .
• The Transformer winding & phase conductor to point of Fault .
543-Protective Conductors .
543– provides information on the Selection of “ BOTH “ type & Cross – sectional Area of Protective Conductors .
Protective Conductors . areconductors provided for the purposes of Safety . protectionagainst Electric Shock .
GenericTerm “ ProtectiveConductors “ :thinking2:
2392-10. as designer(s) . Am making you Aware of the Facts .
Cross-sectional Areas of Protective Conductors .
Thereare two Methods that may be Employed when choosing a Protective Conductor asrequired by Regulation 543.1.1.
TheCross- sectional Areas ( C.S.A. ) of every ProtectiveConductor . other than Protective BondingConductors .
MustBe :-
Selected . in accordance with Regulation 543.1.4. - :icon4:
Or
Calculated . in accordance with Regulation 543.1.3. - :icon4:
2392-10: Yes we still use it in Industry :icon4:
543.2.7. Earthing Tail Requirement .
WhereMetallic Conduit . Trunking . etc is used for a ProtectiveConductor . The Earthing Terminal ofeach Accessory is required to be connected by a Separate Protective Conductor to the Earthing Terminal incorporated in theassociated box ( BackBoxes) or other Enclosure .
Applicationsof Earthing : :vanish:
All Metallicenclosures & Extraneous conduciveparts . are at Equipotential .
Functionsof Earthing :
EquipmentEarth : Path for Fault Current . lowertouch voltage . protection against Electric Shock .
LightingEarth : Low résistance path to diversethe current . Under lighting attack .
TelecommEarth : Signal Earth . reduce noise & interference . stabilize D.C. supply voltage & prevent ElectricShock .
ComputersEarth : Reduce interference . maintain supply voltages .
Typeof Earthing :- :vanish:
SupplySystem – Neutral / Earth .
SystemEarth
ElectricalSafety Earth .
LightingEarth .
GeneratorEarth .
ProtectiveEarth . - Surge arrestor .
Telecom/ Computer Earth .
ShieldingEarth .
IntegratedEarthing System -
ElectrostaticEarth – Clean / room – Hospital .
Factors affect to the EarthImpedance . TT Systems :oops:
Soil.
Weather.
Electrodetype .
Electrodesize .
Near by Utilities .
Electrode in Parallel . -&-s
Distance between Electrode .
:thinking2:TT Systems
EarthRésistance of an Electrode
Soil Exhibits a resistance to the flow an Electrical Current .
Not an “ Ideal “ conductor
Résistance – can never be Zero . betweenthe Earth Electrode & “ True Earth
The résistance between the Earth Electrode & “ True Earth
SoilResistivity in ( Ωm )
Buriedlength of the Electrode in ( m )
Diameter of the Electrode in ( m )
Fault :icon4:
A circuitcondition in which current flows through an abnormal or unintended path .
Thismay result from an Insulation failure or a bridging of Insulation .
Conventionallythe Impedance between Live conductors or between Live conductors & Exposed or Extraneous conductiveparts at the Fault position isconsidered Negligible.
Regulation. Appendix 4 – ( 4D1A ) p/274 :17:
Caremust be taken tie sure that any Conductors’ which is operating above ( 70°C) is terminated into Equipment that canwithstand the higher temperature .
TheBritish Standard only requires that our Equipment is suitable for ( 70°C)
Ambient Temperature mustalways be taken into account .
TheCurrent Carrying Capacities given in the Tables in appendix 4 Calculated for a Cable operating in an Ambient Temperature of ( 30°C ) .
( 4D1A ) for4.0mm[SUP]2[/SUP] – Copper Conductor clipped direct can carry a currentof ( 37A ) at ( 30°C ) Pass a current of ( 37A ) through the conductor it would rise to ( 70°C )
Ambient Temperature were to increase to . ( 40°C ) then theTemperature of the conductor when we passed ( 37A ) through it would rise to ( 80°C )
Side– Effect . of this would be an Increase in Voltage Drop .
The Maximumpermissible operating temperature of Cables are dependent mainly on the Type ofInsulation Material used in the Cable Construction
( 4D1A )
Ambient Temperature ( 30°C ) ◄◄
ConductorOperating Temperature ( 70°C )
Temperature is the Factor which dictates the size of theConductor in relation to the Number of Circuits Installed.
Thermoplastic : ( 70°C ) :44:
Measurement of ExternalEarth Fault Loop Impedance ( Ze ) iscarried out between the Incoming Line & Protective Earth . :19:
Earthing Conductor Detachedfrom the ( MET ) & test probe clipped toit .
Measurementof the External Earth Fault Loop Impedance ( Ze ) at the Origin of theInstallation for compliance with regulation 612.9
EarthFault Loop Impedance :
Live Tests & great careshould be taken when carrying them out .
Thereare Two Measurements for Earth Loop Impedance .
i) One is for External Loop Impedance ( Ze )
ii) Other is for the Circuit Loop Impedance ( Zs )
Bothof these tests are carried out Using an Earth Fault Loop Impedance TestInstrument with Leads & Probes compliant to ( GS-38 )
(Ze ) Earth Fault Loop Impedance :
TheInstallation must be ( Isolated ) – “ Live Test “ ◄◄ -&-s & the Earthing conductor disconnected .
Connectone Lead to the disconnected Earthing conductor& then insert a Probe into the Terminal ofthe Incoming Line .
TheMeasured Value will be ( Ze )
I use the Megger 1552 : Two Leads .
►► Instrument has ThreeLeads then the Third Lead must be connected to the Incoming Neutral ofthe Supply .
Thisis what -&-s want to Hear . ▼
TheEarthing Conductor must be Reconnected beforere-energising the Supply to the Installation .
(Zs ) Circuit Earth Fault Loop Impedance : :19:
Thisis a Live Test . ◄◄ for-&-s 2392-10 - ( At Socket Outlets)
“ Simple“ What is required . The Instrument is plugged into the Socketusing the Lead supplied & the resultRecorded .
TheHow’s & Why’s ??
Wherethe Circuit has NO socket outlets the instrumenthas to be ( Connected ) to the Exposed Terminalsof the Accessories on the Circuit being Tested .
ALL POINTS must be tested & the Highest testresult Recorded as ( Zs ) for the Circuit
“ Certification& Reporting “
Onyour Test result sheet & add the Measured ( Ze ) to the Recorded ( R1 + R2 ) value . Then compare the totalvalue with the Measured ( Zs ) if it is Equal toor Lower then all is Fine .
Ifit is Higher then it may be that there is a Loose Connection & further Investigation is required .
Froma Testers point of View (- The Measured value will often be Less than theCalculated value due to the Presence of Parallel Path.
Measured( Zs ) must be compared to the Maximum value of ( Zs )
From-&-s point of View (- Ensurethat it complies with the Requirements for the circuit disconnection time .
O.S.G.p/13 .
BasicInformation Required . 313.1. Beforestarting Work on an Installation . Etc
ForExisting Installations Electricians’ should Satisfy themselves as to the Suitability ofthe Supply including the Earthing Arrangement. :speechless:
Regulations: Table 41.3 - Maximum Earth Fault LoopImpedance ( Zs )
Table 41.3 -For Circuit Breakers with ( Uo ) of 230V . ForInstantaneous operating giving Compliance with the ( 0.4s )disconnection time of Regulation 411.3.2.2.
BS-EN 60898 . / BS-EN 61009-1
MaximumMeasured Earth Fault Loop Impedance ( Ωs ) Overcurrent Protective Device is a Circuit Breaker .
Table 41.1.
MaximumDisconnection Times ( 0.4s ) - 411.3.2.2.
TheMaximum Disconnection Time stated in Table 41.1. shall be applied to FinalCircuit NOT Exceeding ( 32A ) - The regulations are using the Words . Final Circuit(s)
Apprentices. if we look at Table 41.1. - Maximum Disconnection Time stated in Table 41.1.is for a ( TN- system ) A.C. ( 0.4s )
MaximumEarth Fault Loop Impedance .
TheMaximum Earth Fault Loop Impedance is used to Calculate the available EarthFault Current within an Installation connected at ( Low – Voltage – below 1000V) :17:
***Cont../ Useful Information for Electricians & Apprentices***
Australia
amberleaf,
Dan,
TrueNAS JBOD Storage Server
