Joined
Dec 24, 2016
Messages
404
Reaction score
92
Location
london
1.25ohm external earth fault loop impedance on TN-S supply to building

Supply authority stated our only option is a TT conversion as they will not covert to PME.

What would be my best course of action when converting to a TT as the building is quite old and i do not want a 100ma main switch for diversity reasons and nuisance tripping, so Would it be suitable to convert to TT and have all final circuits in a RCBO with a board charge?
 
What is this SDS adapter as i normally use a club hammer?
[ElectriciansForums.net] Converting to a TT system... possibly
 
I screw an earth rod driving bolt 5/8 into a rods coupler, then use an sds nut driver with the appropriate size socket, drill on hammer and rotostop. Don't expect to be able to use the nut driver and socket for anything else though
 
The DNO are obliged to maintain the earth they have there REG 25 ESQCR. Tell them you will take it up with HSE if they will not. They can put a steel band around the intake cable and braided earth from that. There is no excuse for them not to comply. Kick some arse!

The earth is in place and functioning.
 
Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
Max value for TNS is 0.85 off top off my head. That's what DNO's have to work to. Either it is, or it isn't.
Yes it is. May not be optimal but most likely all OCPDs will not exceed their maximum permitted ao what is the issue?
Incorrect. It's well out of spec for a TNS system. Simple. Argue as much as you like, it's out of spec.
 
1.37 ohms max zs for a32 amp type B so unless your R1+R2 is ridiculously low then your max zs for this circuit will be exceeded.
I do not know what overcurrent protection is involved in this instance nore no of any rcd protection but no one in their right mind should except that ze measurement on that particular earthing arrangement.
 
I who hazard a guess that the DNO fuse would also not disconnect in the required time 5seconds if there was an live to earth fault on the tails.
Same statement could be said about a TT arrangement, however it’s not a TT arrangement at present.
 
Last edited:

Reply to Converting to a TT system... possibly in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Sticky
  • Article
Wicked I've just actually looked through it and it's very smart. Some good stuff in it. There's a tile association company that do a magazine...
Replies
2
Views
315
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
295
  • Article
Hi everyone, Another weekend, another sale! Get ready for colder days with Haverland Radiators, combining efficiency with modern design. Keep...
Replies
0
Views
361

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
929

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top