pencilpusher

Hi

I am about to export TNCS from a dwelling to the detached garage. (The garage is originally a TT system with a poor EFLI, over 200 ohms) I am aware that TNCS can be exported and I am going to do this. There are no extraneous conductive parts in the garage either.

My problem is this: 2.5mm T&E leaves the consumer unit and joins 2.5mm SWA at an adaptable box on the outside wall. It travels 3 meters underground to the garage CU. Ze is 0.22 ohms and my calcs are that the short run of SWA will give a ZS at the garage CU of about 0.28 ohms, ish. That will give me a PFC of about 0.8KA at the garage CU. The SWA has a CPC bunched and I can parallel that with the armour. Fine, BUT when the 1.5mm CPC in the T&E meets the swa, I don't think that is adequate to comply with the adiabatic equation. My calcs give me a minimum cpc of about 5mm sq.

Have I got this right and do you agree I will need to upgarde the T&E meeting the SWA?

I have looked at other threads but they don't quite answer my specific issue.

Thanks

PP
 
To determine the CSA required for a CPC, you need to furnish the type and rating of the overcurrent protective device.
If for instance you intend using a 32A type B MCB, the time/current graphs in Appendix 3 of BS7671, indicates that the PEFC required to provide disconnection between 0.1 and 5s is only 160A.
Your calculated value of 800A will be more than sufficient to to allow the device to operate, and according to the adiabatic equation, will require a minimum CPC CSA of 0.44mm².
 
To determine the CSA required for a CPC, you need to furnish the type and rating of the overcurrent protective device.
If for instance you intend using a 32A type B MCB, the time/current graphs in Appendix 3 of BS7671, indicates that the PEFC required to provide disconnection between 0.1 and 5s is only 160A.
Your calculated value of 800A will be more than sufficient to to allow the device to operate, and according to the adiabatic equation, will require a minimum CPC CSA of 0.44mm².

Thanks Spin. Forgive me for being a muppet but it totally threw me. I will be using a type B 20A RCBO which only needs 100A to operate within 0.1 secs and that gives me a minimum csa of 0.27mm.

Thanks again.
 
Well that depends on what side of the fence you sit on

Plenty of export this and export that guides here, there and at the ESC etc

Shame really :ack2:

I respect your views but as I say, there is nothing wrong with doing so from my side of the fence!
 
Last edited by a moderator:
You can't export a PME earth outside the equipotential zone, check the subtleties of ESQCR & 7671.

You CAN extend the equipotential zone though, thus allowing you to utilise a PME earth in an outbuilding!
 

Reply to CPC size help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
161
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
997
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

totally agree
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top