P
pencilpusher
Hi
I am about to export TNCS from a dwelling to the detached garage. (The garage is originally a TT system with a poor EFLI, over 200 ohms) I am aware that TNCS can be exported and I am going to do this. There are no extraneous conductive parts in the garage either.
My problem is this: 2.5mm T&E leaves the consumer unit and joins 2.5mm SWA at an adaptable box on the outside wall. It travels 3 meters underground to the garage CU. Ze is 0.22 ohms and my calcs are that the short run of SWA will give a ZS at the garage CU of about 0.28 ohms, ish. That will give me a PFC of about 0.8KA at the garage CU. The SWA has a CPC bunched and I can parallel that with the armour. Fine, BUT when the 1.5mm CPC in the T&E meets the swa, I don't think that is adequate to comply with the adiabatic equation. My calcs give me a minimum cpc of about 5mm sq.
Have I got this right and do you agree I will need to upgarde the T&E meeting the SWA?
I have looked at other threads but they don't quite answer my specific issue.
PP
PP