CPC size help

Page 243 isn't viewable....

Interestingly, it does show the use of the manufacturers I2t values in the adiabatic equation that I mentioned earlier.

Using this value is where the 1.2mm minimum value for CPC came from.

Definitely more than one way to skin a cat.

Sent from my BlackBerry 9800 using Tapatalk
 
According to table B7 page 120 0f onsite guide as long as using a 20A class 3 mcb a minimum size protective conductor of 1.5mm can be used if the fault current does not exceed 3KA, I suppose that producing this table the IET have taken account of all what has been disscussed in this thread I2t etc.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Advert

Thread statistics

Created
pencilpusher,
Last reply from
silverfox1,
Replies
63
Views
9,292

Advert

Back
Top