Page 243 isn't viewable....

Interestingly, it does show the use of the manufacturers I2t values in the adiabatic equation that I mentioned earlier.

Using this value is where the 1.2mm minimum value for CPC came from.

Definitely more than one way to skin a cat.

Sent from my BlackBerry 9800 using Tapatalk
 
According to table B7 page 120 0f onsite guide as long as using a 20A class 3 mcb a minimum size protective conductor of 1.5mm can be used if the fault current does not exceed 3KA, I suppose that producing this table the IET have taken account of all what has been disscussed in this thread I2t etc.
 

Reply to CPC size help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
161
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
997
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

totally agree
Replies
12
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top