OP
pencilpusher
Lenny, I have read this previously but I am grateful for you posting it. However, it does not help in telling which answer is correct in my original question. The fact is I have still been given different answers.
To determine the CSA required for a CPC, you need to furnish the type and rating of the overcurrent protective device.
If for instance you intend using a 32A type B MCB, the time/current graphs in Appendix 3 of BS7671, indicates that the PEFC required to provide disconnection between 0.1 and 5s is only 160A.
Your calculated value of 800A will be more than sufficient to to allow the device to operate, and according to the adiabatic equation, will require a minimum CPC CSA of 0.44mm².
To determine the CSA required for a CPC, you need to furnish the type and rating of the overcurrent protective device.
If for instance you intend using a 32A type B MCB, the time/current graphs in Appendix 3 of BS7671, indicates that the PEFC required to provide disconnection between 0.1 and 5s is only 160A.
Your calculated value of 800A will be more than sufficient to to allow the device to operate, and according to the adiabatic equation, will require a minimum CPC CSA of 0.44mm².