View the thread, titled "CPC size help" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Yep, this is a good thread. I get the idea of this now Lenny so thanks for explaining; I was just about to knock an outside wall down to get at my T&E !!

I must admit, I always thought the protective device would not "let through" 0.8kA when its a 20 amp breaker. That is the confusing thing about high currents and time graphs. Surely, a 0.8kA fault current would trip the breaker in under 0.1 secs and the cpc would not "have time" to melt?!

Is that what manufacturers "let through" data is concerned with, how much actual fault current, the device will accept before it actually trips and stops any current causing problems?

Cheers

PP
 
Here's a suggestion:
Using the tables in Appendix 3, for devices other than MCBs.
Starting at 5s, conduct the adiabatic equation using the values in the tables and work your way down to 0.1s.
I think the result will surprise most people.
 
basically, we are fitting far too large cables for various jobs, thus fuelling the ridiculous price of said cable to the delight of the manufacturers and the south african copper mine owners.
 
AFAIC the answer I've given using the manufacturers data is the answer, end of.

Spin is referring to fuses in his post, not your MCB.
 
Last edited by a moderator:
Lenny, I wasn't questioning your answer just the answer to the copper miners taking the p**s. Same thing i suspect!!

The let through data I have found on t'internet (not easy) shows a figure of 19.5. I suspect it is 19.5 something which is why you have quoted as 19500?
 
Last edited by a moderator:
In general, protective devices operate faster, the greater the current.
As such as the current exists for a shorter period of time, there is less heating of conductors.
This results in a smaller CSA being required.
MCBs are an oddity, because they utilise two methods to operate.
An electromagnetic coil and a Bi-metallic strip.
In the tables in Appendix 3, these are represented by the straight line for the electromagnetic coil and the curve for the Bi-metallic strip.
The tables only show the amperage required for the MCB to operate within the times specified by BS7671, 0.1s to 5s.
Without having the manufacturer's time/current curve available, it is quite likely that this Amperage will also cause the MCB to operate instantaneously (within 0.01s).
When you start picking and mixing the values, choosing one that is measured, and another that is tabulated, you will when conducting the adiabatic equation obtain a result that produces a higher value for CSA than is actually required.
If you wish to use the measured value of PEFC 800A, you should not use the tabulated time values in the tables in Appendix 3, but those of the manufacturer.
If you wish to use the tabulated time values from the tables in Appendix 3, then you should also use the tabulated current values.
 
Last edited by a moderator:
So basically, the adiabatic equation should be used during the design stage. If already installed and a measured PEFC taken, the manufacturers data should be used for I2t?
 
Last edited by a moderator:
You can use either the manufacturer's data, or that contained in the tables in Appendix 3.
Just not a pick and mix.
 

Reply to the thread, titled "CPC size help" which is posted in Electrical Wiring, Theories and Regulations on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top