Your welcome, be best you learnt the how tos and why fors
Shame you are not open to discussion :ack2:
Shame you are not open to discussion :ack2:
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
Discuss CPC size help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
There is nothing in BS7671 or ESQCR prohibiting the exportation of a PME earth.
There are problems when the location the earth is being exported to has extraneous-condutive-parts, in sofar as an appropriately sized bonding conductor will be required.
Often this prohibits the exportation due to cost.
Are you really going to export a PME earth ?
Well that depends on what side of the fence you sit on
Plenty of export this and export that guides here, there and at the ESC etc
Shame really :ack2:
Are you really going to export a PME earth ?
Good Luck
How much experience have you with TNCS,PME and TT and exporting earths and the problems associated with it ?
I must admit, to being a Bitter person.
That Larger is just too bland for my liking.
To determine the CSA required for a CPC, you need to furnish the type and rating of the overcurrent protective device.
If for instance you intend using a 32A type B MCB, the time/current graphs in Appendix 3 of BS7671, indicates that the PEFC required to provide disconnection between 0.1 and 5s is only 160A.
Your calculated value of 800A will be more than sufficient to to allow the device to operate, and according to the adiabatic equation, will require a minimum CPC CSA of 0.44mm².
When using the adiabatic equation, what fault current do I use. The actual measured fault current ie 0.8kA in linked thread or the fault current required to trip the CPD which would be much lower
You would use your actual measured fault current if you have it available which would be 800A in this case. What the OCPD requires doesn't come into it.
2.1 Calculation in accordance with Regulation 543.1.3 Calculation uses one of two methods permitted by Regulation 543.1.3:
The adiabatic equation is reproduced as follows, together with the explanation of the symbols used in it, as given in Regulation 543.1.3.
| ||||||||||||||||||||
The adiabatic equation is based on the assumption that the duration of the earth fault current is so short that none of the heat energy produced in the protective conductor escapes before the protective device operates. The assumption, though never true, is reasonably accurate providing the operating time of the disconnecting device does not exceed 5 s, as is normally required by BS 7671. The csa of a protective conductor, where calculated using the adiabatic equation, must be not less than the required value (S) given by that equation. 2.1.1 Values of I and t or I2t for use in the adiabatic equation Source of values of I and t The value of prospective earth fault current (I) to be used in the adiabatic equation is normally determined by calculation, due to the circuit generally not yet having been constructed. The value of operating time (t) for the disconnecting device, for use in the equation, is that corresponding to the value of I, and is ascertained from the time/current characteristic for the device (such as given in Appendix 3 of BS 7671). Source of values of I2t (for situations where the use of separate values of I2 and t is impracticable or unreliable) The use of separate values of I2 and t in the adiabatic equation is impracticable where the value of I is so high that a corresponding value of t is not shown in the time/current characteristic for the disconnecting device. In such circumstances, a value of energy let-through (I2t) should be substituted into the adiabatic equation. The I2t value should be obtained from the energy let-through characteristic for the disconnecting device, published by the manufacturer, which is normally in the form of a line or curve giving maximum values of I2t as a function of prospective current under stated operating conditions. The use of a value of energy let-through (I2t) in the adiabatic equation may also be necessary in the following circumstances, in which the use of separate values of I2 and t is an unreliable basis for calculation:
Assumed position of earth fault Where the disconnecting device is a fuse, the appropriate values of I and t, or I2t to be used in the adiabatic equation are normally those corresponding to an earth fault occurring at the point of the circuit concerned which is electrically most | ||||||||||||||||||||
remote from the supply. This is because the characteristics of fuses of the types considered in BS 7671 are generally such that the energy let-through (I2t) is greater the lower the fault current. The same does not always apply for circuit-breakers, however. It will often be found, from the energy let-through (I2t) characteristic of a circuit-breaker, that for fault currents exceeding a certain value (normally somewhat higher than that causing operation of the device within 0.1 s), the energy let-through (I2t) is greater the higher the fault current. As a general rule, where values of prospective earth fault current exceeding about 1 kA occur anywhere in the circuit, the energy let-through characteristic of the device, obtained from the manufacturer, should be consulted. From this characteristic, the maximum value of I2t for the range of values of prospective earth fault current occurring throughout the circuit should be ascertained, and should be substituted into the adiabatic equation. 2.1.2 Value of k for use in the adiabatic equation Values of k for protective conductors in various use or service, for use in the adiabatic equation, may be obtained from Tables 54.2, 54.3, 54.4, 54.5 and 54.6 of BS 7671. 2.1.3 Protective conductor common to a number of circuits Where calculated, the csa of a protective conductor that is common to several circuits is to be based on the most onerous of the values of earth fault current (I) and operating time (t) (or energy let-through (I2t)) encountered in each of the circuits which share the cpc (Regulation 543.1.2). 2.1.4 Where the application of the adiabatic equation produces a non-standard conductor size Where the application of the adiabatic equation produces a non-standard conductor size, a protective conductor of at least the nearest larger standard csa has to be used. 2.1.5 Canonical form of adiabatic equation Finally, it should be mentioned that the adiabatic equation can be expressed in canonical (basic) form, as given below, in which the prospective earth fault current (I) is not squared, because it is brought outside of the square root sign. |
Reply to CPC size help in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net