Client currently has a 16th edition board with a current operated ELCB 230v 60amp 30mA main switch. He wants a socket radial circuit for his new extension.
My question is, is this switch 17th edition compliant. If I install the required circuit. I know it is the old form of RCD but as it covers the whole installation does it goes against reg 314
Would you recommend a CU change? Or install the required circuit! Bonding to water is present gas is plastic supply, does this still need Bonding.
Appreciate your replies.