L

LlandrilloSpark

I'm running a 30 metre length of three core 16mm armour to feed a garage conversion which could have a high loading.
The cable will be run from the external meter box where I will split the meter tails via a Henley
The problem is There is naff all room in the box and I can't fit a switched fuse in there to protect the armour as the main cut out is 100A
Can I put the switched fuse of another suitable protection device at the other end to protect against overload?
Cheers
 
Well id suggest he utilizes 433.2.2 part (i).

Regards Chris


He could & I'm not disputing that, I mentioned it earlier. The only point I raised was regarding the DNO and their inability to se the wood for the trees. They want (or at least mine do) to see the additional protection within 3M of their service head, end of. They wont be told any different and I just wanted to make the OP aware of it.

BS 7671 isn't the be all & end all.
 
He could & I'm not disputing that, I mentioned it earlier. The only point I raised was regarding the DNO and their inability to se the wood for the trees. They want (or at least mine do) to see the additional protection within 3M of their service head, end of. They wont be told any different and I just wanted to make the OP aware of it.

BS 7671 isn't the be all & end all.

Well just remind them of this;

1 Definition Network ESQCR

Consumer’s installations in buildings are not intended to be included in the definition. Such installations should comply with the requirements of BS7671 Requirements for Electrical Installations or those of other relevant standards. Electrical distribution systems on offshore installations are also excluded from the definition, e.g. oil rigs.

So tell them to concentrate on there network and you will concentrate on your installation to the relevant standards.

As for there equipment in a premise then there is also this;

ESQCR

Equipment belonging to distributors and meter operators which is installed on consumers’ premises must be suitable for itspurpose and safe. Examples of such equipment include: cables, meters, distribution boards, isolators and switches.Such equipment must also be electrically protected by fuses, cut-outs or circuit breakers. For safety and technical reasons the protective device should be situated as close as reasonably practicable to the supply terminals. Where flats are supplied by rising mains, duty holders should ensure that all equipment upstream of the supply terminals at each flat benefit from adequate electrical and mechanical protection.
In order to demonstrate compliance with the requirements of regulation 24(1) duty holders should adopt the standards of construction and installation necessary to comply with BS7671 Requirements for Electrical Installations.

Regards Chris
 
Last edited:
Wouldn't that mean the only protection the 16mm would have is the 100A service fuse? I wouldn't even consider that as an option! I would also be doing everything I could to rcd protect the armoured.
 
I would also be doing everything I could to rcd protect the armoured.

I agree about protecting the submain, but you don't want an RCD at source (Why?) as it would/could trip the whole of the remote installation on an earth fault which is a good 30 M away !, no, RCD's local if required is far better IMO, besides if the RCD was at source would this not contravene the regs wrt circuit segregation ? (314.1).

Unless of course the Installation was TT, and then a time delayed 100mA may be required
 
Last edited:
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:
 
I would have thought the 100A service fuse protecting the 30M run was a big no-no. If someone puts a spade through the SWA, the supply for the whole house is lost until the DNO comes out? Daz.
PS I'm no expert, so feel free to pull this comment to bits :smiley2:

nothing wrong with your comment. a 60A sw fuse is the answer.
 
Hence why you protect the cable using an over-current device.
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz
 
Yep fair enough. Just saw a couple of posts on page 1 that seemed to be saying you don't need the fuse - seemed strange. Daz

The question wasn't should we or should we not install it as obviously we should. We were debating on where it should go in relation to the service head.

Overcurrent protection doesn't necessarily have to be at the origin of a circuit, (433.2 refers) but when it comes to the DNO, they are a law unto themselves so in this instance it would be best IMO to place it at the origin.
 
Just trying to get this straight in my head so apologies!

If the overcurrent protection is at the end of the 30M run, the scenario of a spade through the SWA will not result in the fuse blowing, but will blow the service fuse.

I thought if the 60A switch-fuse was protecting the cable it should go at the origin?

Daz
 

Reply to Distribution circuit question in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
291
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
798
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
828

Similar threads

I might have got lost here, but the rotary iso is rated at 63A so 25mm armoured still wouldn't make the install satisfactory. Assuming everything...
Replies
7
Views
487
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...
Replies
29
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top