View the thread, titled "Distribution circuit question" which is posted in Australia on Electricians Forums.

L

LlandrilloSpark

I'm running a 30 metre length of three core 16mm armour to feed a garage conversion which could have a high loading.
The cable will be run from the external meter box where I will split the meter tails via a Henley
The problem is There is naff all room in the box and I can't fit a switched fuse in there to protect the armour as the main cut out is 100A
Can I put the switched fuse of another suitable protection device at the other end to protect against overload?
Cheers
 
We're talking two different types of protection here I.e overcurrent & short circuit.

Before we were mainly talking overcurrent protection which ad I said previously can be placed anywhere along the circuit, (433.2.2)

Reliance on the suppliers fuse for short circuit is debateable and IMO in this instance wouldn't be accepted by the DNO should they find out.

Sent from my BlackBerry 9800 using Tapatalk
 
Problem Solved

Got a 100mm x 190mm metal clad enclosure with 80A main switch and 63A MCB, its proteus(CEF) so not the best but it will do the job at origin, im going to have to move the mainswitch slightly in the meter cupboard to fit it in but at its the best i can do

cheers for the input, ive enjoyed reading it all!
 
View attachment 10506

And if he was he may have used the attachment as a guide

I never use that table, the one originally posted by Spin in the same ''STICKY THREAD'', is the one to use, and have done for a number of years now. In your link a 16mm SWA cable fails to meet compliance for a XLPE 3 core cable, whereas in the alternative table it DOES comply.... It would also comply in 2 core 16mm form as well!!


Table for 90[SUP]0[/SUP]C Thermosetting SWA cables operating at 70[SUP]0[/SUP]C.

[TABLE="class: yiv965604117MsoTableGrid"]
[TR]
[TD="width: 118"]
Conductor CSA
[/TD]
[TD="width: 118"]
Minimum CSA of SWA to meet 54G
[/TD]
[TD="width: 118"]
CSA of armour 2 core
[/TD]
[TD="width: 118"]
CSA of armour 3 core
[/TD]
[TD="width: 118"]
CSA of armour 4 core
[/TD]
[/TR]
[TR]
[TD="width: 118"]
1.5
[/TD]
[TD="width: 118"]
3.4
[/TD]
[TD="width: 118"]
16
[/TD]
[TD="width: 118"]
17
[/TD]
[TD="width: 118"]
18
[/TD]
[/TR]
[TR]
[TD="width: 118"]
2.5
[/TD]
[TD="width: 118"]
5.7
[/TD]
[TD="width: 118"]
17
[/TD]
[TD="width: 118"]
19
[/TD]
[TD="width: 118"]
20
[/TD]
[/TR]
[TR]
[TD="width: 118"]
4
[/TD]
[TD="width: 118"]
9.0
[/TD]
[TD="width: 118"]
19
[/TD]
[TD="width: 118"]
21
[/TD]
[TD="width: 118"]
23
[/TD]
[/TR]
[TR]
[TD="width: 118"]
6
[/TD]
[TD="width: 118"]
13.6
[/TD]
[TD="width: 118"]
22
[/TD]
[TD="width: 118"]
23
[/TD]
[TD="width: 118"]
36
[/TD]
[/TR]
[TR]
[TD="width: 118"]
10
[/TD]
[TD="width: 118"]
22.6
[/TD]
[TD="width: 118"]
26
[/TD]
[TD="width: 118"]
39
[/TD]
[TD="width: 118"]
43
[/TD]
[/TR]
[TR]
[TD="width: 118"]
16
[/TD]
[TD="width: 118"]
36.1
[/TD]
[TD="width: 118"]
41
[/TD]
[TD="width: 118"]
44
[/TD]
[TD="width: 118"]
49
[/TD]
[/TR]
[TR]
[TD="width: 118"]
25
[/TD]
[TD="width: 118"]
36.1
[/TD]
[TD="width: 118"]
42
[/TD]
[TD="width: 118"]
62
[/TD]
[TD="width: 118"]
70
[/TD]
[/TR]
[TR]
[TD="width: 118"]
35
[/TD]
[TD="width: 118"]
36.1
[/TD]
[TD="width: 118"]
62
[/TD]
[TD="width: 118"]
70
[/TD]
[TD="width: 118"]
80
[/TD]
[/TR]
[TR]
[TD="width: 118"]
50
[/TD]
[TD="width: 118"]
56.4
[/TD]
[TD="width: 118"]
68
[/TD]
[TD="width: 118"]
78
[/TD]
[TD="width: 118"]
90
[/TD]
[/TR]
[TR]
[TD="width: 118"]
70
[/TD]
[TD="width: 118"]
79.0
[/TD]
[TD="width: 118"]
80
[/TD]
[TD="width: 118"]
90
[/TD]
[TD="width: 118"]
131
[/TD]
[/TR]
[TR]
[TD="width: 118"]
95
[/TD]
[TD="width: 118"]
107.2
[/TD]
[TD="width: 118"]
113
[/TD]
[TD="width: 118"]
128
[/TD]
[TD="width: 118"]
147
[/TD]
[/TR]
[TR]
[TD="width: 118"]
120
[/TD]
[TD="width: 118"]
135.3
[/TD]
[TD="width: 118"]
(125)
[/TD]
[TD="width: 118"]
141
[/TD]
[TD="width: 118"]
206
[/TD]
[/TR]
[TR]
[TD="width: 118"]
150
[/TD]
[TD="width: 118"]
169.2
[/TD]
[TD="width: 118"]
(138
[/TD]
[TD="width: 118"]
201
[/TD]
[TD="width: 118"]
230
[/TD]
[/TR]
[TR]
[TD="width: 118"]
185
[/TD]
[TD="width: 118"]
208.6
[/TD]
[TD="width: 118"]
(191)
[/TD]
[TD="width: 118"]
220
[/TD]
[TD="width: 118"]
255
[/TD]
[/TR]
[TR]
[TD="width: 118"]
240
[/TD]
[TD="width: 118"]
270.6
[/TD]
[TD="width: 118"]
(215)
[/TD]
[TD="width: 118"]
(250)
[/TD]
[TD="width: 118"]
289
[/TD]
[/TR]
[TR]
[TD="width: 118"]
300
[/TD]
[TD="width: 118"]
338.3
[/TD]
[TD="width: 118"]
(235)
[/TD]
[TD="width: 118"]
(269)
[/TD]
[TD="width: 118"]
(319)
[/TD]
[/TR]
[TR]
[TD="width: 118"]
400
[/TD]
[TD="width: 118"]
451.0
[/TD]
[TD="width: 118"]
(265)
[/TD]
[TD="width: 118"]
(304)
[/TD]
[TD="width: 118"]
(452)
[/TD]
[/TR]
[/TABLE]
 

Reply to the thread, titled "Distribution circuit question" which is posted in Australia on Electricians Forums.

Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Daily, weekly or monthly email

Back
Top