Guys i'm doing an EICR at the minute. Do hand dryers for public use require RCD protection? Wired in singles in earthed steel pipe, no bath or shower in the room........
 
but on a EICR, the worst he can do is a code C3, or a comment recommending RCD protection.
 
If the hand dryer is hard wired on a TN system and as the cable is conduit run and is not in a room containing a bath or shower then the regulations do not require RCD protection of the accessory.

However probably a good idea anyway!.
 
Shouldnt be coded at all if it's not a requirement of 7671....this is why EICR's vary so much,electricians introduce personal opinions when the ONLY criterior is whether it complies onr not.
 
Shouldnt be coded at all if it's not a requirement of 7671....this is why EICR's vary so much,electricians introduce personal opinions when the ONLY criterior is whether it complies onr not.

Agreed, I missed the earthed metallic pipe bit!, IF its in a bog not a bathroom, NO code could reasonably be given other then an observation.
 
Guys i'm doing an EICR at the minute. Do hand dryers for public use require RCD protection? Wired in singles in earthed steel pipe, no bath or shower in the room........
Depends on the type of installation, I would avoid RCD protection on fixed equipment at all cost, however if TT for just one example then it would need it, whats the earthing arrangements and whats the zs reading?
 

Reply to Do hand dryers require RCD protection in the Electrical Appliances Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
285
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
787
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
804

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
684
Usually if there are only C3 observations it would usually be deemed satisfactory but could be found to be unsatisfactory in unusual...
Replies
15
Views
2K
davesparks
D

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top