Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains
Where is the overload protection for the SWA ???? I asked earlier its a crucial part of the design.
 
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains

OK....reasonable hat on.
No an additional earth electrode is not required if the entire system is connected to a TNCS earth. There are those who suggest it is a good idea though,as it will reduce the risk of voltages appearing on conductive parts in the (highly unlikely) event of a broken neutral on the supply side.
I have never rodded a TNCS installation myself.
Bear in mind that main bonding in the house will have to meet the requirements for a TNCS system,ie minimum 10mm back to the MET.
 
OK....reasonable hat on.
No an additional earth electrode is not required if the entire system is connected to a TNCS earth. There are those who suggest it is a good idea though,as it will reduce the risk of voltages appearing on conductive parts in the (highly unlikely) event of a broken neutral on the supply side.
I have never rodded a TNCS installation myself.
Bear in mind that main bonding in the house will have to meet the requirements for a TNCS system,ie minimum 10mm back to the MET.



Nice one, thanks for the help. :) the day you stop learning is the day you give up so another thing learned. Thanks :)
 
This is what ive been trying to point out from the start several times .... he gives the impression he's using the DNO cutout fuses as upfront protection or he doesn't know the difference between a switchfuse and an isolator.


Oh come on!! .............. He MUST know the difference - he's a spark isn't he?? ......

.............


....... Isn't he?????!!! .. :confused: ... :thinking:
 
This is what ive been trying to point out from the start several times .... he gives the impression he's using the DNO cutout fuses as upfront protection or he doesn't know the difference between a switchfuse and an isolator.

I know you were, but your subtle approach wasn't getting anywhere so I thought I'd try a more direct approach
 
Hi all, you all seem to be having a good laugh. Method of earthing is TNCS in meter cupboard 25m from house, swa 25mm has been run into an isolator with tails out in the meter cupboard, just wondering if an additional earth stake would be required nearer the house. Just want to cover my arse now before the board come out to liven it up.
Thanks for your brains

I do hope that 25mm SWA cable is 3 core, or it won't comply for bonding purposes at the house. That is, the steel wire armouring will not be have a sufficient CSA to comply for bonding purposes, it will only comply as a CPC!!
 

Reply to do I need an earth stake - metre is 25m from fuesboard in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
296
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
841

Similar threads

Yes the first bit is just standard wiring, TNS lead cable into cut-out, cut-out to meter, meter to DP isolator, top of isolator is sealed as per...
Replies
8
Views
1K
  • Question
With what looks like only 5 circuits you can probably put a little 5 way garage consumer unit in there if money is tight
2
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top