Earth and bonding cable checks-any tools available? | Page 2 | on ElectriciansForums
Discuss Earth and bonding cable checks-any tools available? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
A cooker installer, is an installer who can safely install electric, gas and dual fuel cooking appliances.
All of them have a MFT (Fluke 1652) and perform polarity, EFLI pre and post installations, but they are now expected to confirm reg 132.16.
I don't get the negative posts here, I just was looking for some pointers to make their lives a bit easier.
Why all the negatives vibes?
Heres the answer for you then.
Firstly you need to check that the pipes are exteanepus conductive parts ( the test for this is explained in GN8). Now as this requires you to disconnect any bonding conductors you need to safely isolate the whole supply to the installation, but you know how to do thos already dont you?
If it requires bonding
Use the correct meter (according to GN3) to check the end to end resistance of the cable, now this has to be done with cable disconnected at both ends and with the whole supply still isolated from previous test, the result must then comply with the value within GN8
The cable must then be correctly sized for the earthing system in place and size of the incoming neutral.
yeah exteanepus, that'll really throw him lol
Because you should be capable of teaching them how to do this if your claim earlier is correct.
I hope they carry out all the dead tests too and in the correct order, and understand the results also.
if these cooker installers are expected to check earthing and bonding, then they should have been trained how. you could help by telling them where the connections are if they are not obvious.
I could easily quote from a GN etc, but those publications are intended for a competent person.
Perhaps I should teach them all the adiabatic calculation?
Reply to Earth and bonding cable checks-any tools available? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Was there any toast to go with the beans? Just joking I think that you ment beams and not beans I am dyslexic and simple mistakes tend to jump out...
2 3