This is for the people still in or has just left their electrical education or for those of us that need a refresher in domestic earthing arrangements. It's all very well looking at prity diagrams in college and in books but its different when your out in the field for the first time. Hope this thread helps you and I hope that other members will post up their pictures of main incomers/earthing so others can learn and understand this subject better. I wish I could refer to something like this when I was in college.



First of all we have 3 types of earthing arrangements, TN-S, TN-C-S and TT.

TN-C-S
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


This is where the main earth cable from the main earth terminal (met) is connected to the neutral at the suppliers main fuse. A good way to remember the name of this arrangement is to think of the C meaning COMBINED.


TN-S
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


This is where the main earth cable from the met is clamped or solderd to the steel of the SWA or the led outer sheath of the incoming supply cable. Again a good way to remember this is to think that the S stands for SHEATH.

TT
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's


The main earth cable from the met is connect to an earth electrode (aka earth rod). This is because not all properties are supplied with a TN system by the supplier so we have to insert a rod into the ground.


Notice how the earth cable on the TN systems go back to the main incomer, one goes to the main fuse (TN-C-S) and the other goes to the incoming cable (TN-S). If the main earth cable doesn't go back to the fuse or incoming cable it will be a TT. This is the simplest way I can put it without going into extended detail.



Now that we've seen some prity diagrams (am I starting to sound like a teacher lol) we will now look at real world photos that are not as straight forward as the diagrams.


First example, is it a TN-S or a TN-C-S or both?

[ElectriciansForums.net] Earthing Arrangements Explained + Photo's
 
Last edited:
I have that one and I have "2750 - Legend Of A Locomotive" which is a fictional story about an A3 Class Gresley Pacific named "Papyrus" that I've seen many times written by H.C. Webster. (I think I have some for diesel as well but let's not go there!)

Somehow, by fair means or foul, Tidyboiler managed to find a copy for me.



[ElectriciansForums.net] Earthing Arrangements Explained + Photo's

Actually, Tidyboiler stayed up until 3.45 am bidding against some Cockney for this book!!! I had to sell my other kidney and firstborn to pay for it! :love:
 
Right you are, not to assume.
After obtaining some temporary seals from the DNO I looked inside the carrier and this is what I found.

Brush
30 Amp
60 LR
Certified
440V AC 4
BS88 - 1952
Class 3
Made in England

The print on the fuse had faded so there may be errors in the above info.

The DNO were contacted again and they're sending an engineer to address the issue.

Anyway, can anyone identify its breaking capacity?
 
If you have a neutral connected to an installations earth terminal (eg PME/TNC-S) then the incoming supply cables metallic sheath connection must be disconnected. Especially important where a supply cable is suppling both TN-S and TNC-S earthing arrangements!! eg, ....where the DNO cable is in the process of being PME'd....
emm? just wondering why?Does the sheath not need to be bonded too? I cant make out the writing on the service head,how do we know this presumably later conversion to TNC-S hasn't been done on the fly by mr diy sparky. I was thinking it could be left in place to be sure to be sure.
 
Just because you asked Archy

How it was explained to me at the EMEB collage.

Around each of the earth rods there will under earth fault conditions be a voltage gradient in the ground. In order for the MV and LV to be interconnected the LV earth electrode must be <2Ώ. Higher and the site is referred to by the DNO as hot and no direct MV→LV earth connection is allowed.
Therefore the LV earth has to be moved away from the MV equipment earth. This is to prevent a MV earth fault migrating to the LV system.

My drawing for OH supply
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's



DNO drawing for ground mounted
[ElectriciansForums.net] Earthing Arrangements Explained + Photo's
I think these overhead earthing systems are being done away with due to copper theives leaving the rural customer without an earth
 
emm? just wondering why?Does the sheath not need to be bonded too? I cant make out the writing on the service head,how do we know this presumably later conversion to TNC-S hasn't been done on the fly by mr diy sparky. I was thinking it could be left in place to be sure to be sure.

Any exposed PILCS sheath to be wrapped in amalgamating tape. No problem mixing TT with TN, but it's not good Practice to mix Two Different types of TN systems....

Most DNO converted systems will be provided with a PME Warning Sticker. If in any doubt call the DNO to find out, just don't expect them to be quick in rushing round to check!! lol!!
 

Reply to Earthing Arrangements Explained + Photo's in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
300
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
812
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
869

Similar threads

  • Question
A bit like saying plumbers makes good electricians. 🥴
Replies
10
Views
2K
  • Question
I'm assuming the cable will have to be cleated well to hold it in place anyway, as a stuffing gland ain't going to hold it tight like a SWA gland...
Replies
10
Views
706

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top