I did not know that Engineer54.
522.8.10 a cable buried in the ground shall incorporate an earthed armour OR metal sheath or both, suitable for use as a protective conductor.
A split concentric cable has neither of these elements, thus does not conform to the requirements, of this regulation...
Can you expand please?
Concentric cables, split or otherwise are the same as any normal cable. With the split concentric cable it is basically the same as a T&E with bare earth conductors, except that all the conductors are laid out concentrically around a central conductor core.
Therefore you can't direct bury in the ground, this type of cable needs to go into a mechanically protective duct. Likewise using this cable in the fabric of a building, it needs to conform to all the requirements that say a standard T&E cable would. ..eg buried less than 50mm in walls etc will require additional RCD protection unless other mechanical protection is afforded...
Just looking in JW P203
Three types of cable may be installed underground
1 armoured or metal sheathed or both Fine
2 PVC insulated concentric type. .....Not unless is has an armouring, or an overall metal sheath incorporated, which to my knowledge they don't!!
3 Any suitable cable enclosed in conduit or duct which gives at least the same degree of mechanical protection as an armoured cable. Fine