EICR and RCD's. Is it a C2 or C3? | Page 4 | on ElectriciansForums

Discuss EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

Joined
Mar 19, 2019
Messages
9
Reaction score
0
Location
London
Hi,

My EICR is a C2 because the consumer unit does NOT have RCD's.
Is it correct?
My last EICR five years ago stated RCD as recommended.
What's changed?
The flat is on the 2nd floor built in 1997!
The electrician has quoted for a NEW Consumer Unit.

Thanks

Victor
 
Why would a landlord be responsible for stupid children and lazy parents?
If you have to ask that question then I don't think you'd really be able to understand the answer so probably best not to go into it.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
 
According to the tick sheet there is supplementary bonding in the bathroom so no rcd required there. There is also IR values in L-N column, so everything got disconnected, all lamps removed etc to preform this test - I don't think so.
I would complain to NAPIT as the standard of the report is poor with unwarranted C2s.
All said though a board upgrade is a good recommend.
Supplementary bonding does not remove the requirement for RCD protection of bathroom circuits. 30mA RCD protection of bathroom circuits may well remove the requirement for supplementary bonding though.
 
Without personally inspecting the property it’s difficult to know what has been discovered or missed by the previous inspection. I may issues a code 2, if for example,
1. Socket installed too close to a sink which can potentially be splashed
2. Any signed of water ingress
3. TT earthing system have no RCD protection
4. Outside socket (balconied) or potential to plug in and use an device outside.
5. High Zs reading not protected by RCD
6. No mechanical protected for cables (concealed <50mm, in metal framed partition, or otherwise)
7. Socket within 3m of zone 1
Or any other general safety conserns that want a risk assessment for admission of RCD (reg 411.3.3)

The fact that it’s probably got code 3 5 years ago and the recommendation goes ignored. Most people translate c3 to satisfactory and just ignore then until they get worse or C2s.
 
Last edited by a moderator:
If you have the eicr from 5 years previous did the spark ask to see it? As he’s ticked date of last inspection unknown but you say 5 years?
 
Last edited:
The tick sheet says there is RCD protection for the bathroom circuits.
Q1 it says u have 10 mmm main tails these are usually 25 or 16 min
If they are 10mm this is a C2 as they are undersized
Q2 report says u have AFDDs and surge protection
Defo not
Q3 did he inspect below the floors and above ceilings
Q4 did he carry out R1+ R2 tests as the numbers are exactly ZS-ZE
Q5 cable type 1 on report there is no type 1 it should be A
The values on the report are wrong 5.88 ??
You should send that report to NAPIT and ask for their comment and if possible post the response on the forum,,
The quality of testing is always a question raised ,
There is no rcd test results on his results
And he says there is rcd test notifications labels
 

Reply to EICR and RCD's. Is it a C2 or C3? in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
381
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
961
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top