I have noticed recently on the forums various opinions on what does and doesn't warrant observation regarding bathroom bonding to previous 16th regulations,
Would be interested to gather opinion on the following scenario.....
2 Bed 6th floor flat wired in PVC singles through in-situ pvc conduit through building fabric. Consumer unit is a 16th edition unit consisting of BS 3871 type 2 MCB's with no existing RCD protection on circuits covering the bathroom. There is 10mm2 main protective bonding to both gas and water services to the premises and the Zs values of the circuitry within the location are compliant.
The bathroom has a class 1 sufficiently i.p rated light on a 5A MCB and a downflow heater circuit located outside zones protected by a 15a MCB.
There are no visual signs of 4mm2 earth or bs951 clamps to either the pipework or run to circuits, howerver, a continuity test gives the following results.
Between all extraneous pipework within the location 0.00ohms
Between pipework and metal light carcass 0.44ohms
Between pipework and downflow heater circuit cpc 0.26ohms.
Taking all the above into account would this therefore warrant
1/ A C2 departure as there is no RCD and no visual signs of bonding......or
2/ A C3 departure as No RCD protection present but bonding confirmed as adequate by continuity tests using the formula R<_ 50v/ Ia.
Thoughts and reasons for your answers would be interesting, and no this isn't somebody looking for an answer to an exam question!!
Would be interested to gather opinion on the following scenario.....
2 Bed 6th floor flat wired in PVC singles through in-situ pvc conduit through building fabric. Consumer unit is a 16th edition unit consisting of BS 3871 type 2 MCB's with no existing RCD protection on circuits covering the bathroom. There is 10mm2 main protective bonding to both gas and water services to the premises and the Zs values of the circuitry within the location are compliant.
The bathroom has a class 1 sufficiently i.p rated light on a 5A MCB and a downflow heater circuit located outside zones protected by a 15a MCB.
There are no visual signs of 4mm2 earth or bs951 clamps to either the pipework or run to circuits, howerver, a continuity test gives the following results.
Between all extraneous pipework within the location 0.00ohms
Between pipework and metal light carcass 0.44ohms
Between pipework and downflow heater circuit cpc 0.26ohms.
Taking all the above into account would this therefore warrant
1/ A C2 departure as there is no RCD and no visual signs of bonding......or
2/ A C3 departure as No RCD protection present but bonding confirmed as adequate by continuity tests using the formula R<_ 50v/ Ia.
Thoughts and reasons for your answers would be interesting, and no this isn't somebody looking for an answer to an exam question!!