415.2.2 states that SB is effective if R≤50/Ia
Agreed
But you don't agree that if the R is already ≤50/Ia no more bonding is required. Why would it be?
______________
and
542.2.1 states that a fixed conductor or an extraneous part may be used as a SB conductor so if the parts already satisfy R≤50/Ia then 415.2.2 is met and no Supplementary(additional) Bonding is required.
How do you intend to apply that to the requirements of 701? The SB is required to be connected to the Protective Conductor Terminal of the location? And i assume 543.2.1?
I'm not sure what you mean by keeping asking about 701. That's what we are discussing.
If not required for the above reason then it does not apply.
543.2.1 merely lists parts which may be used as bonding including an e-c-p (pipe) and fixed conductor (cpc).
________________
This would seem to be the only thing we do disagree about so I will ask again - if this is not so and SB must be applied regardless thus reducing the impedance to negligible why is 50/Ia ever mentioned?
Not too sure what you mean, i think you need to be specific with regard the installation. If we take an agricultural location 705,say a large metal shed, if two conducive parts are effectively connected do we need to SB the two, no, your interpretation in that instance is correct, but not with regard 701.
What I mean is - you are stating that SB must be applied (where I think not) in which case the resistance between the parts will always be near negligible so why did they think up the 50/Ia rule. In your world the bathroom would need to be massive to get anywhere near 50V.
________________
With only a lighting circuit in the room and all parts connected by up to 5m. of 4mm² the touch voltage would only be 30x0.023 = 0.69V.
Even with a 40A shower it would only be 200x0.023 = 4.6V.
What if a greater current was to flow through the bonding conductor
That's not the purpose.
All we have to consider is the greatest Ia of the bathroom circuits.
That is the highest current that may flow from a touchable exposed part before the disconnection of the current - 5x6A for lighting or e.g. 5x40A for shower.
To ensure the voltage drop from this exposed part to another part that may be touched is a maximum of 50V, therefore 50V/If ≥ R
________________
So why is the limit set at 50V when this would never occur if everything must be bonded regardless?
Belt and Braces, ensuring no fortuitous connections, and as you have stated 50 V is what they regard as safe
Then why, if that is already met by the installation, are you insisting on reducing it further with additional supplementary bonding which is not required.
The fortuitous connections to which you refer are the very parts to which you want to connect the extra un-required bonding.